The dangers of condensation! | on ElectriciansForums

Discuss The dangers of condensation! in the UK Electrical Forum area at ElectriciansForums.net

Darkwood

Arms
Joined
Jun 15, 2009
Messages
13,711
Reaction score
10,231
Location
West Yorkshire
Got a callout from a mate saying his light are out and all circuits are on, also he thinks something smells funny so given the latter info I said it best I pop over and check it out, now considering I went to look at the lighting issue, what I found in the board was an example of the issues of condensation running though the breakers over the years.
The burnt out mcb was a 40amp shower supply but the heat burnt through the adjacent main switch into the live pole and a 32amp mcb on the other side, all effected breakers were rendered useless welded in the on position and taking power direct through the mainswitch regardless of its position.
All uneffected mcb's of this heat damage were stuck physically in the on position as the mechanics has siezed with the damp although the lighting did operate internally but couldn't reset.
I raided by box of spares and replaces the heat damaged devices and the lighting, disconnected temp' other circuits ready for a board change.
The cellar has a extract fan design to remove the damp air but it was never switched on.
I'll be passing this job on to a mate who can sign off the new board as I don't do domestic and I'm too busy for a guv job (which I never do ;) )

[ElectriciansForums.net] The dangers of condensation!
[ElectriciansForums.net] The dangers of condensation!
 
To be fair the issue was not the brand nor the tightness of connections that usually are a factor, it was good old H2O and I've seen this happen to the best of brands under the same conditions.. the damp penetrates the mcb, corrodes the contact points creating high resistance, it tends to show on high current circuits before low current ones if effecting multiple devices and that was exactly what happened here.
the hardest part of doing a temp' repair is getting the gear out when it rusted solid on terminations like the busbar, took alot of persuation with a ratchet set and a tapping hammer to shock them loose without reeming the heads out.
You can see in the pic that the terminals are corroded too.
 

Reply to The dangers of condensation! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey, Mccb is set to 1 so would have been rated at the 160 amp. Which is considerably less than the capability of both the cable and the...
Replies
4
Views
1K
  • Question
Youre in the same boat as me. I was previously with niceic and later on, napit. No issues. I didn't bother finishing my nvq3 as in 2010 during the...
Replies
7
Views
3K
  • Question
Well congratulations my friend and if you ever need any more help you know where to get the right advice
Replies
20
Views
4K
  • Question
4 bed house, 1 candle per bedroom.....
2
Replies
26
Views
4K
Just in case I just bought a Megger MIT 330 on a great deal on evilbay as a stand alone tester too for every eventuality ! It was Westwards fault...
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks