Greetings all.

My neighbour has just had a garage built in the shape of an old barn.
We live in the sticks and I guess the only way the architect could get it through planning was to make it this way.
It's in keeping with the surrounding area.

As he is my next door neighbour he has asked me to do the electrics.
The supply is a 2.5mm SWA buried underground.
The system is a TN-S with the transformer on a pole in the field out back.

I will have a quick look at it later but I have a couple of small queries if anyone can enlighten me.

As the supply is SWA which means it is earthed in a metal housing does it need to be RCD protected.
I don't think it does, I am thinking of a distribution circuit you know like they supply street lights with and a 5 second disconnection time.
As the supply is TN-S from an underground supply cable I don't think exporting an earth from the main house will be a problem.
I could TT it and would probably get low results for EFLI but I would prefer to keep the distributors earth.
Can anyone see any problems with exporting a TN-S earth?

The other question is I want to encase all the cables in black galvanized metal conduit to give it a more pleasant look but I am little concerned about the sockets.
What would members consider to be the best and most attractive sockets and switches to put on.
They would be metal surface mounted supplied by cables in black enameled conduit.
Has anyone any recommendations?

I will take some pictures in due time but I wondered if anyone has ever done a job like this.

Many thanks.
 
No need for the dist circuit to be RCD protected, but you will want to earth the metal armour at the supply end.

As you're considering metal conduit I'd go for metal clad fittings, particularly in a garage. Less likely to be damaged.

When you check out the garage, see if there's any extraneous metal in the structure as that would need bonding back to the MET if you're using the suppliers earth. So that would mean running an larger bonding cable as well as the SWA (2.5mm would not be large enough for bonding I suspect).
 
Greetings all.

My neighbour has just had a garage built in the shape of an old barn.
We live in the sticks and I guess the only way the architect could get it through planning was to make it this way.
It's in keeping with the surrounding area.

As he is my next door neighbour he has asked me to do the electrics.
The supply is a 2.5mm SWA buried underground.
The system is a TN-S with the transformer on a pole in the field out back.

I will have a quick look at it later but I have a couple of small queries if anyone can enlighten me.

As the supply is SWA which means it is earthed in a metal housing does it need to be RCD protected.
I don't think it does, I am thinking of a distribution circuit you know like they supply street lights with and a 5 second disconnection time.
As the supply is TN-S from an underground supply cable I don't think exporting an earth from the main house will be a problem.
I could TT it and would probably get low results for EFLI but I would prefer to keep the distributors earth.
Can anyone see any problems with exporting a TN-S earth?

The other question is I want to encase all the cables in black galvanized metal conduit to give it a more pleasant look but I am little concerned about the sockets.
What would members consider to be the best and most attractive sockets and switches to put on.
They would be metal surface mounted supplied by cables in black enameled conduit.
Has anyone any recommendations?

I will take some pictures in due time but I wondered if anyone has ever done a job like this.

Many thanks.

A 2.5mm SWA is pointless waste of money, use a minimum 4mm 3 core SWA, at least you will be future proofing to some extent. 3 core, as then you can use the 3rd core as your bond and the armour as your CPC. In reality they will both be connected to the garage EMT !!anyway...

I personally wouldn't use black enamelled conduit in a garage, due to corrosion over the years. Nothing to stop you using Black PVC conduit, or indeed galvanised conduit, that will match the metal clad switches and socket outlets.
You have a choice to either use standard type metal-clad fitments or the full sized metal clad, where you can use standard metal switch and outlet fronts of your neighbors choice...
 
Must admit, mine's done in plastic conduit and just about to do another the same way (still with metal clad accessories). You may even find that 4mm isn't large enough for bonding but at least that'll take you up to around 40A possible supply (xlpe).
 
If you have other services in the barn (water, structural metal) which require bonding then I would suggest you are best off making the installation TT by using an earth electrode (and RCD of course!) at the garage end. Else you will end up needing to confirm the minimum size of the bonding cable and may choose a larger size SWA than you actually need. If there is no local bonding required then simply export LNE in a 3 core armoured cable.

The size of the SWA should be determined by considering the maximum demand for the garage (now and in the forseeable future) and the length of the cable run to determine voltage drop. 2.5mm SWA may well be perfectly adequate if it can comfortable meet the above 2 requirements.
 
Thanks guys really helpful, I like the pictures Topquark.

The supply is already there and is a 2.5 mm SWA although not sure if it has its own CPC or just the armoring.

There are no extraneous metallic parts introducing earth potential, just a concrete floor and an empty building although this may change.

I noticed a gas bond of 6mm attached to the gas pipe outside the main house which is very close to the barn.

Getting a new 6mm or 10mm bonding cable from the barn to the fuse board in the house would be impossible without digging the whole patio up so if he were to introduce a water supply I could attach a bond to the existing gas bond( not strictly correct as per regulations, needs to be an unbroken cable) or just TT the whole thing.

It looks like a nice job.
 
If you don't have 3 cores in the SWA you could work out the CSA of the armour (use a micrometer to measure the diameter of one strand, apply Pi*r*r to get its CSA, then multiply by the number or strands). Then check this against Table 54.7 in the regs.

TT is probably easier!
 
the flaw of the abve plan is that CSA of conductors is nominal. That means that the manufactureres will conduct tests to see how much current the conductor will take ect, and then assign a nominal CSA. if you look at different manufacturers of cable,the actual measured CSA will be different. it probably wont me much but there will be slight differences
 
If no extraneous metalwork in the garage, then just use what you have, the armouring of the SWA cable. Don't even consider TT'ing this garage there is really no need whatsoever!!


If your neighbour later wants to have a water supply in there, tell him to pipe it in, in Plastic pipe. lol!!!
 
couldnt agree more. The garage is probably one of the most dangerous parts of a domsetic electrical installation, due to the use of power tools, the possible dam[p and wet environment, and the alomst certain use of gear outside the equipotential zone. with all of this considered, why would you consider using the least protected of all supplies (TT). RCD's can and do fail.
 

Reply to The old barn electrics in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
764
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

  • Question
https://www.edwardes.co.uk/products/mk-k1257whi-logic-plus-1gang-13amp-non-standard-dp-switch-socket?gad_source=1&gclid=EAIaIQobChMI7POp_pHFhgMVk5J...
Replies
1
Views
393
In Theory that’s a good argument but if you will be adding or moving switches or sockets or adding lights you’ll more than likely end up needing a...
Replies
7
Views
548

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top