As has already been stated an 'either or' question is far too simplistic, both rings and radials have their uses.
I think it is worth summarising what I see as some disadvantages of both circuits.

Existing rings...(on EICR's for example) are an absolute pain to verify. Unknown layouts and non-textbook readings mean verifying the possible presence of spurs from spurs, interconnections etc is time consuming and involves much dismantling. Most of us use plug in testing adaptors which often produce odd readings due to contact or switch resistance on ancient outlets, the only certain way is to drop the points and use probes straight onto terminations, disruptive, time consuming and damaging to surface finish. Real time constraints when carrying out EICR's at acceptable cost mean ring circuits are often not properly verified and the inspector has to make judgement calls on whether the circuit is correctly wired. That said I love testing my own rings and calculating whether measured readings are spot on!
As far as radials go there was a long thread on here a while back where an OP stated rings should be outlawed because they are often abused by Kev the kitchen fitter and DIY Dave, his point was radials are much safer.
But unskilled persons being unable to correctly alter a ring is not a reason for banning it, ban Kev and Dave...not the ring!!
That point of view also ignores the potential danger of a radial. One bad or broken connection of the cpc may result in every downstream point working and apparently ok but not having an earth.
I think the safest circuit of all is a radial serving one point from a 16 or 20a OCPD, but the practicalities of that with the number of points modern properties require make it a non starter, not only for the capacity of DB required, but for the sheer quantity of wiring involved.
It is though an interesting phenomenon that many people are completely incapable of altering a ring, and finishing up still with a ring, and not just Kev and Dave. A ring is one of the simplest of all circuits, just a loop of cable which starts and finishes at the same point, and yet it continually seems to generate utter incompetence.
 
People think rings are bad , I recently watched a video of a guy wiring his house in America and he put lights and sockets on the same circuit using the same sized cable and kept calling it ‘roughing’ in his wiring...

it was blooming rough and at every point he stripped the cores back & twisted the bare copper earths together and shoved them in the back of each box so he had just the L & N to connect later
 
People think rings are bad , I recently watched a video of a guy wiring his house in America and he put lights and sockets on the same circuit using the same sized cable and kept calling it ‘roughing’ in his wiring...

it was blooming rough and at every point he stripped the cores back & twisted the bare copper earths together and shoved them in the back of each box so he had just the L & N to connect later
and no doubt a proliferation of fire nuts. on another forum, predominantly American, several members praise their silly wire nuts and condemn wagos.
 
People think rings are bad , I recently watched a video of a guy wiring his house in America and he put lights and sockets on the same circuit using the same sized cable and kept calling it ‘roughing’ in his wiring...

it was blooming rough and at every point he stripped the cores back & twisted the bare copper earths together and shoved them in the back of each box so he had just the L & N to connect later

Yeah, I was watching the ideal international sparky championship. Aussie, Canadian, American and a Chinese fella in the final. Someone in the comments section asked where the British entry was. The comments were “Anyone who uses Rings, are not invited” and the like. These foreign morons have no idea of the concept. They probably would have trouble wiring one.
 
Yeah, I was watching the ideal international sparky championship. Aussie, Canadian, American and a Chinese fella in the final. Someone in the comments section asked where the British entry was. The comments were “Anyone who uses Rings, are not invited” and the like. These foreign morons have no idea of the concept. They probably would have trouble wiring one.

I thought you were going to say a joke; at the sparkie championship, there was an Aussie, Canadian, American & Chinese's sparks in the competition.

When asked, where were the British entries, they said they weren't invited as they would run rings around us. :)
 
Real time constraints when carrying out EICR's at acceptable cost mean ring circuits are often not properly verified and the inspector has to make judgement calls on whether the circuit is correctly wired. That said I love testing my own rings and calculating whether measured readings are spot on!
As far as radials go there was a long thread on here a while back where an OP stated rings should be outlawed because they are often abused by Kev the kitchen fitter and DIY Dave, his point was radials are much safer.
But unskilled persons being unable to correctly alter a ring is not a reason for banning it, ban Kev and Dave...not the ring!!
That point of view also ignores the potential danger of a radial. One bad or broken connection of the cpc may result in every downstream point working and apparently ok but not having an earth.
The problem with properly verifying a ring is not lost on a radial either (for the record, I think spurs off a ring are the Devil's work and should be you last resort).

Say you have a 32A radial in 4mm, how often would an EICR check it had not been extended in 2.5mm for much the same risk as a double-spur on a ring?

Yes, the usual radials on 20A might be safe for 2.5mm but it is the same underlying problem - if some idiot has extended a circuit badly it is not always apparent from the readings.

I guess checking the worst case Zs is OK for the MCB is probably good enough for most cases, but complete verification of an unknown is a costly and difficult situation in both cases.
 
The problem with properly verifying a ring is not lost on a radial either (for the record, I think spurs off a ring are the Devil's work and should be you last resort).

Say you have a 32A radial in 4mm, how often would an EICR check it had not been extended in 2.5mm for much the same risk as a double-spur on a ring?

Yes, the usual radials on 20A might be safe for 2.5mm but it is the same underlying problem - if some idiot has extended a circuit badly it is not always apparent from the readings.

I guess checking the worst case Zs is OK for the MCB is probably good enough for most cases, but complete verification of an unknown is a costly and difficult situation in both cases.
Indeed, and one of my bugbears on this forum is those who advise punters to have an EICR because it will identify any problems. No it wont necessarily.... and those of us tasked with carrying out EICR's are not helped by the creation of unrealistic expectations of what an EICR can identify.
 
I think the ring is for the more technical minded. The maths in it are great. Really it is not for amateurs so I can see why dumbing down is the way to go as with so many things today.
I don't quite understand that statement.

The "radial" in the general sense might often be used for all sorts of strange loads so calculating its safe parameters is a bit of a challenge at times.

The radial for a couple of 13A sockets is fairly easy but typically you would see 2-3 MCB sizes possibly used, and 1.5 (dodgy) / 2.5 / 4mm choices depending if it is one, a few, a lot of sockets (or quite long).

The RFC on the other hand, if you keep away from the Devil's spurs, is really simple for 99% or so of cases:
  • Use 2.5mm cable
  • Use a 32A B MCB
  • Loop the cable round from MCB, to every 13A socket, back to same MCB
  • Keep that length below 96m (or look closely at the OSG & check your DB Ze)
Yes, the RFC is dumb choice if you only have a couple of sockets at a remote-ish area, but for most general house wiring it is simple and effective.

I really think if either of them is difficult for someone to grasp then they ought not to be doing it though! But that applies to a lot of things in life.
 

Reply to The Ring is dead, long live the Radial!⚡ in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Why aren't you asking them?
Replies
5
Views
862
  • Question
Tech has totally complicated 'control' Customer wants something controlling. First job is to figure out the best method
    • Funny
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top