thermal derating factors | on ElectriciansForums
Discuss thermal derating factors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
R
rasell
When calculating a thermal insulating rating factor from Table 52.2 [523.7] if the figure is between two of the given numbers do you go up to the next figure or down? For example if the insulation was 150mm would you count it as 200mm (derating factor 0.63) or 100mm (derating factor 0.78).
Usually I round up for safety, but the regs say that if the insulation if equal or bigger than 500mm to use a rating factor of 0.5, so I was not sure what to do when a figure is in between two values in the table.
Table 52.2
if the cable is surrounded by thermal insulation for less than 50mm = no derating factor
50 to 100mm = 0.88
100 to 200mm = 0.78
200 to 400mm = 0.63
400 to 500mm = 0.51
and from the text above the table over 500mm = 0.5
I asked the NICEIC about this and the simle answer was split the factor, so for your example 150mm the factor would be 0.70 in round figures
Reply to thermal derating factors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
nicebutdim
N