Hi all,

Im bookedon the 2391-2 soon, and im reading through the course notes that i got from the kind gents on here, and workinmg through the examples.

Im trying to work outif the cable will withstand the thermal shock of a short circuit.

If i were to work out the PSCC, and then apply this to the adiabatic, and the resulting size comes bvack as less than that of the phase conductor, then is the thermal withstand ok?

eg, PSCC of whole job= 6Ka.
30A 3036 fuse,
6mm cable 25m long

impedance of L-N external = 230/600= 0.038 ohms.

r1+rn of 6mm cable is 6.16mohm/m = 0.154 ohm

total impedance of L-N= 0.154 + 0.038 = 0.192

fault current = 230/0.192= 1197.92A


square root
adiabatic = 1197.2 sq x 0.1
115

answer= 3.29mm (less than the 6mm phase conductor)
 
Hi all,

Im bookedon the 2391-2 soon, and im reading through the course notes that i got from the kind gents on here, and workinmg through the examples.

Im trying to work outif the cable will withstand the thermal shock of a short circuit.

If i were to work out the PSCC, and then apply this to the adiabatic, and the resulting size comes bvack as less than that of the phase conductor, then is the thermal withstand ok?

eg, PSCC of whole job= 6Ka.
30A 3036 fuse,
6mm cable 25m long

impedance of L-N external = 230/600= 0.038 ohms.

r1+rn of 6mm cable is 6.16mohm/m = 0.154 ohm

total impedance of L-N= 0.154 + 0.038 = 0.192

fault current = 230/0.192= 1197.92A


square root
adiabatic = 1197.2 sq x 0.1
115

answer= 3.29mm (less than the 6mm phase conductor)

Thats pretty much it
 
Im trying to work outif the cable will withstand the thermal shock of a short circuit.

Surely withstand should be calculated as a duration of time? Having to assess the effects of fault current on a given size conductor, with consideration of it's achievable disconnection time.

t = (k2 x S2) / I2

so with the values you have..

t = 1152 x 62 / 1197.922 = 0.3 seconds.

Therefore your disconnection time being 0.1 seconds means thermal withstand will be achieved (0.1s < 0.3s).

This is just my take on this.


I've enrolled myself on this course as well recently (want to achieve it before it disappears) so any course material/notes would be very gratefully received.






widdler
 
Surely withstand should be calculated as a duration of time? Having to assess the effects of fault current on a given size conductor, with consideration of it's achievable disconnection time.

t = (k2 x S2) / I2

so with the values you have..

t = 1152 x 62 / 1197.922 = 0.3 seconds.

Therefore your disconnection time being 0.1 seconds means thermal withstand will be achieved (0.1s < 0.3s).

This is just my take on this.


I've enrolled myself on this course as well recently (want to achieve it before it disappears) so any course material/notes would be very gratefully received.


widdler

Yep, ....Based on initial and final conductor tempretures.
 
Surely withstand should be calculated as a duration of time? Having to assess the effects of fault current on a given size conductor, with consideration of it's achievable disconnection time.

t = (k2 x S2) / I2

so with the values you have..

t = 1152 x 62 / 1197.922 = 0.3 seconds.

Therefore your disconnection time being 0.1 seconds means thermal withstand will be achieved (0.1s < 0.3s).

This is just my take on this.


I've enrolled myself on this course as well recently (want to achieve it before it disappears) so any course material/notes would be very gratefully received.






widdler

Same same, there's several ways, they all tell you the same.
 
Same same, there's several ways, they all tell you the same.

Well obviously as it's just transposition of formulae.
But if a question asks you to assess thermal withstand from a fault between Live conductors, you want to verify the time. Not use a formula designed for sizing of "Protective conductors".
 
I've enrolled myself on this course as well recently (want to achieve it before it disappears) so any course material/notes would be very gratefully received.

Widdler

I've got literally 100s of pages of notes, exam papers & project from about 2004 you can have.
They are all scanned images in zipped files, 11 files, biggest nearly 11Meg.
I'll happily email them to you if your email can handle it (some can't I think)
PM me your email address if you're interested.

All the reg references are to the Big Blue Book, but still good reading with loads of worked examples.

Andy
 
Well obviously as it's just transposition of formulae.
But if a question asks you to assess thermal withstand from a fault between Live conductors, you want to verify the time. Not use a formula designed for sizing of "Protective conductors".

Really, And whats the time that a fault between live conductors must disconnect?

Regards Chris
 

Reply to thermal withstand in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
397
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top