I

Inteificio

Hi,

I am getting issues with thermocouple readings getting messed up by magnetic interference from live wires.

What kind of spacing is needed between an unshielded thermocouple wire and 2.5mm cable to minimise these problems?

Thanks,

Peter
 
What type of thermocouple arrangement do you have. Is the thermocouple driving something directly or is the thermocouple connected to a pc board as an input sensor? Is it an RTD such as pt100, if so is it a three wire system with reference or just 2 wire?
 
That is part of the issue, I am very light on information!

It is a two wire system and polarised. It goes in to small PCB control unit. The temp range we use it in is 50-90. (We wire an apolar thermocouple to the same PCB for our cold stuff).

I would assume that they have filters on this circuit as the interference problem is VERY rare, but still comes up occasionally.

My obvious next step is to speak to the PCB manufacturer, but was wondering if there were any regs or relevant advice!

Thanks,

Peter
 
I'm not based in the UK but I doubt this would be covered by general electrical or building regs.

I would suggest either you'll need to re-run the CAT5's with a greater degree of separation or replace them with shielded and bond the braid to the services earth. Depending on the existing earth integrity maybe use a dedicated earth spike if necessary to earth the braid.

You could also try converting it to a three wire system which from experience is less prone to interference but this would depend on whether your control board supports the three wire system.

Apologies in advance, it's difficult to be more specific without more info I'm afraid.
 
Ok, more info (but still not much).

Two wire 'k' type thermocouple, board only takes two wires.

I could calculate the distance that a current would be induced, and put it outside the thermocouples sensitivity range, but as it would induce AC in to a DC circuit I am clueless.

Thanks,

p.s. This is not CAT5. Just two wires twisted at the end.
p.p.s. I know it is annoying when someone asks a question with limited info, but someone must use thermocouples and know from experience how far to space them!
 
It's not so much annoying as just difficult to help. Can you even tell us what type of machine it is? How long is the wiring between the thermocouple and the pc board? How far does the thermocouple wiring and the 2.5 electrical cable run together? Are the two cables running side by side in straight lines or do they vary in distance and criss cross each other in trunking for example? What are the original symptoms that led you to believe that induced interference is the problem?
 
We use this thermocouple in varying devices from large industrial fridges to ovens.

Cable is at most 3 metres long.

We had a MAJOR issue recently where we were getting a false reading from one of the couples (device kept on heating, temp stayed same, not good).

When I was called in to assist, the other sparky had tried everything but magnetic induction, so that was my first step.
Wires running outside device, no issue; wires running in the device, fixed reading.

I want to go back to our designers saying we need spacing of Xcm between the live and thermocouple wires, give us enough room!
 
I ran a few searches through my collection of ISO regs and I didn't find anything relevant. Did you check out the ENC directives suggested by Netblindpaul?
We had a MAJOR issue recently where we were getting a false reading from one of the couples (device kept on heating, temp stayed same, not good).
This type of problem is far more likely to be an intermittently faulty thermocouple or control board. I really don't see induced voltages over a length of a few meters being your problem. I've seen SCADA systems where unshielded sensor wiring is actually cable strapped to electrical cables for over 50 meters and there's still been accuracy within 0.5%.
If you're still convinced that induced voltages are the problem then the first thing to do before you start retrofitting a machine that's in production would be to prove it. To start with I would use a working machine and extend the thermocouple wiring to at least double its normal length and experiment with running it alongside a 2.5 electrical cable for varying lengths and monitor the accuracy of the control board. If the results remain constant then you're probably barking up the wrong tree.

Another quick fix option would be to install an external braid to the thermocouple wiring and ground it. You could try this on your faulty machine, if the fault persists then you've pretty much ruled out induced interference as being your issue.
 

Reply to Thermocouple spacing in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Thank you for the speedy response! Have seen them on top of plaster in steel conduit before but guess it's not a common desire to have wires...
Replies
2
Views
615
Hi there -sorry I see that I've been missing messages from you because they are sometimes concealed by advertising. Perhaps it's easier if you...
Replies
20
Views
2K
H
  • Article
need a new shower but my hot/cold pipes are reversed! Hi All I need some advice as to a replacement power shower and there are a few problems I...
Replies
0
Views
188
harrygee
H
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
532
I am living in the north of Thailand outside of the big city. That means in the rainy season we have multiple times per week power outages...
Replies
0
Views
373

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks