Hi all

I have just completed an electrical installation consisting of 2 ring circuits, 3 lighting circuits, fire alarm circuit and a heating circuit. All went well apart from the heating circuit.....

I have installed 2 electric thermostatic panel heaters, a 500w and a 750w one. They are in two offices and within 10m of the distribution board. The total load therefore is about 5.5A. I decided on a B6 MCB, 1.5mm twin&earth cable on a radial circuit and connected then via individual FCUs. I used a 3A fuse on the 500w and a 5A fuse on the 750w heater.
All dead testing , continuity, insulation resistance, polarity etc was all ok. Live testing was also ok.

My problem is this....
As soon as the 750w heater asks for power, i.e. turning the thermostat up, it trips the RCD but MCB does not trip. I did try a bigger MCB but same response.

I have spoken with technical support at Dimplex and told them the wiring design. They advise it could be a faulty heater and to return it.
Before I do this does anyone else have any other thoughts as to why this would happen...

I am probably missing something really simple but can someone please advise as soon as possible.

Thanks
 
--A well earthed metal sheet-- (Sheet is a good word)
Not sure about dimplex but some cheap ones not much more than a metal sheet with " Electric blanket wire"
Held down by alloy tape .
Usualy get a nice hole in tape if no RCD !
(I was very dissapointed - cheap in china ? )
Tech has moved on - 3M tape very sticky .
2x power settings 2x circuits .....
( I'm hoping some one will correct me and )
( say things have got much better -mats/pads ? )
 
You specifically state that when the 750w powers up, the RCD trips... does the same thing happen when the other unit powers up? Are they both on the same thermostat? If not, is it possible the wiring in the stat is wrong?
 

Reply to Thermostatic panel heaters in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
709
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
795
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top