My first wiring of sockets in a radial and I've not put the 2nd CPC in to make the CPC be a ring, in accordance with figure 7.6 on the OSG.

I guess I'm going to have to take up the floorboards and run a single of CPC...?

How do you all wire your Radial Socket circuits?


Ta,

Si
 
Ah that's a relief.

Oh! I've just seen that too, for circuits between 3.5mA and 10mA, yeah?

Thank you. I didn't THINK I was doing it wrongly, but then I saw that reg and started doubting my self.

Thank you Malcolm and IQ
 
Sorry, I don't have my regs book with me on my day job, please can you clarify or define?

It's lounge sockets circuit.

Where a socket outlet circuit is expected to have a protective conductor current in excess of 10mA (in normal service) then additional requirements are needed for the integrity of the CPC.

That's what section 7.6 of the On-Site Guide is applicable to.
 
its handy to keep your books with you in van or boot of car allways handy to refer to

I work in IT support by day, but yes, the BRB is in my car. I found my OSG in my rucksack under my desk though, so had a quick look and found that indeed I had mis-understood section 7.6

I was going to look in the BRB at lunch, but thought I'd message you all here first, as I was unable to find anything after a quick perusal of the OSG.

But thank you all anyway.
 
Mr Si, you sound a lot more conscientious and knowledgeable than a lot of 'qualified' sparks I know.

Fair play for even bothering to check, most would just say "Ahhh it be fine".
 
I work in IT support by day, but yes, the BRB is in my car. I found my OSG in my rucksack under my desk though, so had a quick look and found that indeed I had mis-understood section 7.6

I was going to look in the BRB at lunch, but thought I'd message you all here first, as I was unable to find anything after a quick perusal of the OSG.

But thank you all anyway.

well done!
 
I work in IT support by day, but yes, the BRB is in my car. I found my OSG in my rucksack under my desk though, so had a quick look and found that indeed I had mis-understood section 7.6

I was going to look in the BRB at lunch, but thought I'd message you all here first, as I was unable to find anything after a quick perusal of the OSG.


But thank you all anyway.
That's a lot of abbvs, mil int?
 

Reply to Think I just made a boo boo in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
93
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
889
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Very technical :D
    • Like
Replies
9
Views
583
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top