This Isn't Right is it? | on ElectriciansForums

Discuss This Isn't Right is it? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

acvc

-
Joined
Jun 1, 2008
Messages
435
Reaction score
26
Location
Ulan Bator, Ulaanbaatar, Mongolia, Mongolia
This morning I went round to a flat in central/north Bristol , a friends son, girlfriend and friend have just moved in, he wanted me to have a look at the electrics. So, this is what I found .......

First floor flat with a car repair garage below.

Mains head couldn't be located - don't know general characteristics.

Entering the flat is a 10mm 6242Y, into a 100mA RCD isolator, 16mm tails from isolator to c/u (old Wylex BS3871).

the rcd has a
10x20mm opening cut on the top where the tails come out;

the (4mm) earth from the 10mm doesn't enter the RCD enclosure but is twisted together and taped round, with a 6mm single core earth conductor to the c/u.
the water heater over the bathroom sink trips the rcd when used;
there is no supplementary bonding to the shower;
no supp bonding to the water heater over the sink in the bathroom;
there's a non IP light fitting 400mm from the shower;
there's a pullswitch for the light in zone 2 also;
there's a smashed up socket with live exposed parts and a Zs of 2.04ohms;
four sockets/fcu's loose on the wall, a couple with 4mm min gaps;
socket for washing machine is directly under the washmachine waste pipe-hooky thing;
no PAT test labels on any appliances;
control knob broken off wall heater in sitting room;
no smoke detector in kitchen or any bedrooms;
only smoke detector is top of stairwell in flat - no detector between flat door and front door to street ( a corridor of 15m plus a staircase);

(This is apart from the fridge door not closing, none of the room doors closing properly, the toilet cistern broken).

Apart from the broken socket, all Zs were within limits and the RCD tripped within times as well.

These poor kids had to pay a month's rent (ÂŁ600), a month's rent in advance, and an agency fee of ÂŁ200 for this!

The person from the agency clearly stated that all of their dwellings had up to date electrical safety checks done and were safe.

OK they are all young and foolish and have got themselves in to a bit of a situation. I've given them a written list of 'observations' made at the flat to give to the agency, stating that I am a registered domestic installer and politely stating that there are "issues" in relation to the Wiring, Fire and Building Regulations. As I was not asked by the landlord or agency to look at the installation as I thought I'd keep it polite and friendly in the first instance, saving the threats for if they don't act on the probs.

Any suggestions or comments ladies and gents?
 
get them to contact the national landlords association and explain the situation make sure your there to give any technical advise on the installation. some of these private landlords and housing associations want stringing up, all they are bothered about is money and couldnt give a ---- about peoples safety.
 
The flat sounds poorly maintained; the agency and landlord should be called to account.
Code 1 the rcd
The broken socket is a code 1.
Pull-cord I would code 2 (only because there isn't an immediate danger).
Washing machine outlet code 3 ~ normal operation shouldn't see water gushing out but a blockage is possible (if not likely)
Smokes and emergency lighting needs further investigation (surely a survey & certificate by a competent person is required)
Supplementary bonding not necessary if the CU has 30mA rcd's ~ seperation also required to satisfy the reg: 314.1 (iii) (pg 39) "take account of danger that may arise from the failure of a single circuit"

Have a look at this document it may also offer some extra leverage.
 

Attachments

  • ESClandlords-Oct09[1].pdf
    689.1 KB · Views: 24

Reply to This Isn't Right is it? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top