Evening Lad's
When testing ZE today on a TN-S supply I got 561 Ohms , upon further investigation I noticed the supply cable had a nice break in the outer sheathing about half way down! and it had some weird looking liquid/gel on it, am I right in assuming this would be the cause of the high ZE ? as when I clamped on to the lead before the break I got 91 Ohms. I had another job to attend so it was left with another sparky who did some other test and later on told me Western Power where on their way. :dunce2:
When testing ZE today on a TN-S supply I got 561 Ohms , upon further investigation I noticed the supply cable had a nice break in the outer sheathing about half way down! and it had some weird looking liquid/gel on it, am I right in assuming this would be the cause of the high ZE ? as when I clamped on to the lead before the break I got 91 Ohms. I had another job to attend so it was left with another sparky who did some other test and later on told me Western Power where on their way. :dunce2: