I'm in the process of rewiring a large portion of a commercial premises. I know this business very well as have attended many times for maintenance/repairs.
Although the works are significant there was no new load being added.
I also know the sector so know how equipment is used, what is on, for how long and in conjunction with what else.
The site is TP&N TN-S its only one phase in use on a 100A fuse and a single phase meter.
An OSG load assessment would give a figure in the order of 260A.
My, better informed, assessment comes in at 140A peak and very intermittent load.
There are no visual signs of overload.
There is a lot of cycling equipment with high inrush and some constant loads that keep a realistic baseline figure around 60A (electric ovens, immersion, and heating)
Enough background?
Came in today to three new 10A AC/Heater units, two to replace two 5A units and one new unit, 20A of additional load.
The customer will pay for needed works but I don't want to rip them off.
My advice to them will be that although overloaded on paper the installation functions at the current load level so not overloaded in reality but is perilously close.
Any additional load is not encouraged but if you must then we need to get the other two phases on line and split the load up.
This will mean a new meter, isolator and TP board.
Does this seem a reasonable approach?
Although the works are significant there was no new load being added.
I also know the sector so know how equipment is used, what is on, for how long and in conjunction with what else.
The site is TP&N TN-S its only one phase in use on a 100A fuse and a single phase meter.
An OSG load assessment would give a figure in the order of 260A.
My, better informed, assessment comes in at 140A peak and very intermittent load.
There are no visual signs of overload.
There is a lot of cycling equipment with high inrush and some constant loads that keep a realistic baseline figure around 60A (electric ovens, immersion, and heating)
Enough background?
Came in today to three new 10A AC/Heater units, two to replace two 5A units and one new unit, 20A of additional load.
The customer will pay for needed works but I don't want to rip them off.
My advice to them will be that although overloaded on paper the installation functions at the current load level so not overloaded in reality but is perilously close.
Any additional load is not encouraged but if you must then we need to get the other two phases on line and split the load up.
This will mean a new meter, isolator and TP board.
Does this seem a reasonable approach?