Hi all

Been asked to quote on this consumer unit change (see photo). Wondering what people's thoughts are on the earthing situation. As can see it is tns but earthing doesn't look to clever to me. It's stranded ali by looks of it. Not sure of CSA of it, looks like could potentially be 10mm at a push. The tails are 16mm and not sure on main fuse size. Could this potentially be compliant? It's likely I may need to relocate new consumer unit as limited for space so in an ideal world would take the main earth into wall mounted block and then from here to consumer unit and to water and gas. As can see from photo the gas is bonded straight from service cable also at the moment.

Any clarification on this would be appreciated.
[ElectriciansForums.net] Thoughts on this consumer unit change
 
Last edited by a moderator:
You'll need to sort out that g/y earth connection from the incoming cable. That earth clip on lead is a no no. Where does it go, bonding or what?
 
Where does the MICC on the left go to?

Looks like the Bare tinned copper go a copper band / screw and nut on the supply Westwood10
Well spotted. Is it feeding something else, off another phase?
...and how is it earthed?
Straight from fuse(s).... not isolated?
 
Last edited:

Reply to Thoughts on this consumer unit change in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
952
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
668
loz2754
L
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top