Hi all
Been asked to quote on this consumer unit change (see photo). Wondering what people's thoughts are on the earthing situation. As can see it is tns but earthing doesn't look to clever to me. It's stranded ali by looks of it. Not sure of CSA of it, looks like could potentially be 10mm at a push. The tails are 16mm and not sure on main fuse size. Could this potentially be compliant? It's likely I may need to relocate new consumer unit as limited for space so in an ideal world would take the main earth into wall mounted block and then from here to consumer unit and to water and gas. As can see from photo the gas is bonded straight from service cable also at the moment.
Any clarification on this would be appreciated.
Been asked to quote on this consumer unit change (see photo). Wondering what people's thoughts are on the earthing situation. As can see it is tns but earthing doesn't look to clever to me. It's stranded ali by looks of it. Not sure of CSA of it, looks like could potentially be 10mm at a push. The tails are 16mm and not sure on main fuse size. Could this potentially be compliant? It's likely I may need to relocate new consumer unit as limited for space so in an ideal world would take the main earth into wall mounted block and then from here to consumer unit and to water and gas. As can see from photo the gas is bonded straight from service cable also at the moment.
Any clarification on this would be appreciated.