Hi all

Been asked to quote on this consumer unit change (see photo). Wondering what people's thoughts are on the earthing situation. As can see it is tns but earthing doesn't look to clever to me. It's stranded ali by looks of it. Not sure of CSA of it, looks like could potentially be 10mm at a push. The tails are 16mm and not sure on main fuse size. Could this potentially be compliant? It's likely I may need to relocate new consumer unit as limited for space so in an ideal world would take the main earth into wall mounted block and then from here to consumer unit and to water and gas. As can see from photo the gas is bonded straight from service cable also at the moment.

Any clarification on this would be appreciated.
[ElectriciansForums.net] Thoughts on this consumer unit change
 
Last edited by a moderator:
Well spotted. Is it feeding something else, off another phase?
...and how is it earthed?
Straight from fuse(s).... not isolated?
Photo is not that clear but if go ahead with job will obviously sort any isolating/fusing issues out. Looks like coming out of our single phase and is interlinked somehow with our meter and what ever that device is on left? Any clue what this is?
 
If the incomer is the bottom one, with the earth attached, then that's pretty normal for old earthing by the dno.

They are obliged to provide and maintain the earth only if it was there previously, as it is, there is an earth; so they comply with their obligations.

I would fit the new cu as normal but add a MET with 16mm^2 between the cu and MET, and a 10mm^2 between the MET and the existing bond where it connects to the cable incomer, and connect the twin 7/44 to the MET.

That way your (customer's) side is in every way compliant, you could also contact the dno and say you don't believe their existing earthing is being maintained properly as it is high resistance, they may follow up and fit a newer earth connection between your MET and their cable.

You could use the poor arrangements associated with the shared/interlinked supply to get them there.
 
If the incomer is the bottom one, with the earth attached, then that's pretty normal for old earthing by the dno.

They are obliged to provide and maintain the earth only if it was there previously, as it is, there is an earth; so they comply with their obligations.

I would fit the new cu as normal but add a MET with 16mm^2 between the cu and MET, and a 10mm^2 between the MET and the existing bond where it connects to the cable incomer, and connect the twin 7/44 to the MET.

That way your (customer's) side is in every way compliant, you could also contact the dno and say you don't believe their existing earthing is being maintained properly as it is high resistance, they may follow up and fit a newer earth connection between your MET and their cable.

You could use the poor arrangements associated with the shared/interlinked supply to get them there.
Thanks Julie
 
I guess this is a flat and the MICC is the upstairs supply. Under ESQCR reg 24 the DNO must maintain an adequate earth. Having said that, an adequate earth to us and them are two different things. I maybe would get my micrometer out and measure their earth but again guess is they are equivalent to 5mm² an adiabatic could settle the adequacy of them. Ideally I would want to see an earth marshalling point and get rid if that BS951 clamp and have it in the MET/marshalling point. I am sure you wont have to bring out the big guns unless you get a jobsworth in the office, but if so elevate to the supervisor and tell them what you need.
 
I guess this is a flat and the MICC is the upstairs supply. Under ESQCR reg 24 the DNO must maintain an adequate earth. Having said that, an adequate earth to us and them are two different things. I maybe would get my micrometer out and measure their earth but again guess is they are equivalent to 5mm² an adiabatic could settle the adequacy of them. Ideally I would want to see an earth marshalling point and get rid if that BS951 clamp and have it in the MET/marshalling point. I am sure you wont have to bring out the big guns unless you get a jobsworth in the office, but if so elevate to the supervisor and
Well spotted Vertigen. Your correct there is actually a property above. So does it look like they have taken neutral from our first head and took a phase from head 3. I'm intrigued by what that box is next to our meter? And the link that looks to be between it
 
No seals on two of the phase carriers, I see and it's not long since the other one was done, so did the 'engineer' know about the other neutral.
 
Watch that earth bond when you take it off....for damage to the lead sheathing. If so, that could be used to get DNO involved, also.
I would get the DNO to take it off when they are sorting the other earth clamp out it is not worth the risk at any level of something going wrong
 

Reply to Thoughts on this consumer unit change in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
668
loz2754
L
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top