Been asked to install some power in a basement in a commercial building to supply some temp computers are floor is on the 2nd floors 4 floors above the basement taking into account the mezz floors so it will be a tricky run.
So we have to come off the landlord board in the LV switchroom.
I was thinking of running a 4mm swa on a 40A type C MCB into a metal merlin gerin board then from the board run 2x 4mm 32A radials on tray supported to the ceiling. then prefabing some tray and unistrat then mounting the sockets onto that.
The landlord has asked for and isolator to be installed nxt to the board so when the desk are removerd after 6weeks we can look it off the monitor furture use on the ccts.
any thoughts