i went to look at a new development yesterday that was in the middle of second fix stage,bit of a strange set up and wanted your thoughts and what regs have been contravened

external meter cupboard
3core 16mm swa terminated into plastic switched fuse then ran to consumer unit inside
terminated directly into plastic CU
inside core used as the main earth terminated into earth bar in the consumer unit
16mm earth taken from earth bar which then Is terminated onto the swa armouring by a bonding clamp to provide an earth.

just seems like an absolute mess and a long winded exercise rather than just using a metal clad switch fuse
 
How is the armour terminated at the switch fuse end? A proper gland should be installed on one end as far as I am aware, a 951 clamp is not sufficient. The use of plastic instead of metal is not an issue, it would be more solid and a better job in a metal clad board, but as long as the s/fuse and CU casings are not all twisted it is not breaking any regs.

Others on here will be able to give a more definitive answer as some of the above may not be entirely correct...I consider myself still learning..
 
How is the armour terminated at the switch fuse end? A proper gland should be installed on one end as far as I am aware, a 951 clamp is not sufficient. The use of plastic instead of metal is not an issue, it would be more solid and a better job in a metal clad board, but as long as the s/fuse and CU casings are not all twisted it is not breaking any regs.

Others on here will be able to give a more definitive answer as some of the above may not be entirely correct...I consider myself still learning..

There should be an SWA gland at both ends.

In the op's situation it would have been easy enough to fit the banjo supplied with the gland at the time of installation.
 
There should be an SWA gland at both ends.

In the op's situation it would have been easy enough to fit the banjo supplied with the gland at the time of installation.

Yep, it would have been easy as you say.

I thought it was the case of the armour having to be properly terminated and earthed at one end as a minimum. Not ideal I know, nor good workmanship, for the sake of 15 minutes extra work....
 
134.1.1 "good workmanship by skilled or instructed persons and proper materials shall be used in the erection of the electrical installation. The installation of electrical equipment shall take account of manufacturers' instructions".

BS951 bonding clamps are designed for clamping on to solid pipes. The force required to make a reliable tight joint on to a SWA cable would effectively deform the cable and may loosen over time due the continued deformation of the cable.
 
134.1.1 "good workmanship by skilled or instructed persons and proper materials shall be used in the erection of the electrical installation. The installation of electrical equipment shall take account of manufacturers' instructions".

BS951 bonding clamps are designed for clamping on to solid pipes. The force required to make a reliable tight joint on to a SWA cable would effectively deform the cable and may loosen over time due the continued deformation of the cable.

Precisely...but sadly,there are so many people flouting this specific point,others view the plentiful examples,and accept it as conforming.

Inspected one this week,where installation was similar to the OPs',and the clamp had been fitted 150mm from the end,with SWA sheath removed just enough to allow clamp band...very neat and tidy...very wrong :blush5:
 
Who needs a BS951 clamp! [ElectriciansForums.net] thoughts please
 
That's an interesting picture, 100A main switch owned by electricity supplier not to be touched by average spark, a struggle to fit a switch fuse in which should be metal and they are bigger... and not to mention shoddy termination on the swa...
 
looks like a temp supply to a site wired by builder monkeys.
that isolator switch is to be touched by average spark to save them pulling the fuse.
terminate that swa into a small metal box alongside meter cabinet, bit of a squeeze but a switch fuse can go in there too.
 

Reply to thoughts please in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
411
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top