three phase 2 pole rcd keeps tripping | on ElectriciansForums

Discuss three phase 2 pole rcd keeps tripping in the Electrician Talk | All Countries area at ElectriciansForums.net

I

iceman

hi chaps i had a call off a guy today frm his commercial warehouse, sayin his rcd keeps trippin, the rcd is on a 3 phase 2pole with 250A 30mA trip i tested it and all seems fine, but it in the office his running 12 pcs server plus all the usual kitchin appliences, this suggests the tripping possable overload , i reken he neds a higher rated rcd, i was thinkin mabe goto 300A with a 63mA trip wots ya thoughts on this:cool:
 
hi chaps i had a call off a guy today frm his commercial warehouse, sayin his rcd keeps trippin, the rcd is on a 3 phase 2pole with 250A 30mA trip i tested it and all seems fine, but it in the office his running 12 pcs server plus all the usual kitchin appliences, this suggests the tripping possable overload , i reken he neds a higher rated rcd, i was thinkin mabe goto 300A with a 63mA trip wots ya thoughts on this:cool:
Confused by the 3ph 2pole bit isnt it 3 or 4 pole? that aside I.T. equipment by the nature of the electronics dump waste electric to earth 'noise' the combination of all the servers is your obvious culprit here exceeding the operating value of your 30mA trip.
Fitting a 100mA should cure the problem but then you will have to fit individual rcbo's with 30mA trip where needed.
This is assuming they is no existing fault causing the rcd to trip in the first place.
 
it is 3 phase but the rcd is on 2 of the phases hence 2 pole , the sockets in question are on a ring final circuit, so you suggest i replace the rcd with a 100mA trip but wot rating would you use, and then replacing the the circuit breaker with an 30mA rcbo?
 
it is 3 phase but the rcd is on 2 of the phases hence 2 pole , the sockets in question are on a ring final circuit, so you suggest i replace the rcd with a 100mA trip but wot rating would you use, and then replacing the the circuit breaker with an 30mA rcbo?
My apologies never come across a 3ph 2pole, without knowing the dist board loading etc i still doubt its an overload problem so fitting the same rating should be fine but clamp the dist board supply to confirm this and as i mentioned before you need to have individual 30mA protection but this will only bring the problem to this rcbo so possible new circuit design to have the servers over different circuits thus reducing the accumulative leak on any one rcd.
 

Reply to three phase 2 pole rcd keeps tripping in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
153
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
518
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
459

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top