Three Phase Board 230V | on ElectriciansForums
Discuss Three Phase Board 230V in the UK Electrical Forum area at ElectriciansForums.net
Dizzy_Maskell
Just after people's opinions seen this a few times and although not incorrect still makes me think:
Three phase board 8-12 ways usually linked out to run on a single 230V supply.
Seen second hand boards converted using bus bar to make in affect a 36 way single phase board.
Always have been properly done e.g labelled and all circuits ok but just wondered how common it is as I am coming across it in a few places now and seems a practical way of having loads of circuits in a single DB.
PS everything done safely correct circuit protection, earth loop etc
I quite often fit a 3 phase board when I only have a single phase supply as I find them nice to work with and a 4 way 3 phase board has much more room than a standard 16way board. Nothing wrong with doing it this way so long as you fit a manufacturers phasing kit and label correctly.
I’ll break my silence on this.
Bear in mind the neutral conductor in a three phase board is rated according to this calculation.
In = √((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))
The combined line conductors in your bodged up board will be three times the size of the neutral.
It’s OK so long as your total cumulative load over the three paralleled phases doesn’t exceed the normal rated current of one phase in normal use.
Don’t they teach electrical theory any more?
I can not imagine in many circumstances where this is used this would happen,
Good point well made though, id better start taking out all the boards where i used the 10 63 Amp breakers :)
But surely, if for instance you had a three phase board with a manufacturers link fitted to turn it into a single phase board and then said board was fed with say a set of 25mm tails, the above equatition doesn't come into play at all.
Similar, IIRC, there is also the issue of harmonics, you should have seen the current waveforms I got off a power analyser last week, a 3yr old could have drawn a better sine wave than they looked like!!!
These problems & issues are real & out there NOW.
Remember & I can't at this time of night, but Triplen & 5th harmonics add to the current in the N?
Can someone else confirm.
Probably the best statement in the world (NOT) IYKWIM! ;)
Reply to Three Phase Board 230V in the UK Electrical Forum area at ElectriciansForums.net
Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...