I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have had answers from 4mm to 50mm cross section from various pages on the internet so you can understand I am a bit confused.
There are two main cables to consider. The first is the incoming main that is about 50m long. It is a 36kVA three phase installation with the Linky on the external garden wall and the cable buried in a flexible duct underground. The second is the feed from my 15kW PV panel generation fed back to the Linky then onward to the electrical mains. This is about 35m long also buried.
I calculate (using some software I have) 16mm2 for the incoming main and 6mm2 for the PV panels. Can you let me know if these sizes seem right or not please?
Finally, what should I be assuming as the max current for a domestic installation. Some say 60 Amps, some say 100 Amps which of course makes a difference in the required cable size. I know we have 100Amp breakers in the UK but I am not sure (and cannot definitively find) what the requirement is here in France.
For the house, 36 kVA divided by say 410V (assuming loss from 415) gives a max load of 88 Amps. For the PV feed 15kW divided by 415 V (post inverter) gives 36 Amps.
Below is my software output for the main cable:
50m Length Calculation for Three Phase cable
Any and all advice welcome, TIA,
Geoff
There are two main cables to consider. The first is the incoming main that is about 50m long. It is a 36kVA three phase installation with the Linky on the external garden wall and the cable buried in a flexible duct underground. The second is the feed from my 15kW PV panel generation fed back to the Linky then onward to the electrical mains. This is about 35m long also buried.
I calculate (using some software I have) 16mm2 for the incoming main and 6mm2 for the PV panels. Can you let me know if these sizes seem right or not please?
Finally, what should I be assuming as the max current for a domestic installation. Some say 60 Amps, some say 100 Amps which of course makes a difference in the required cable size. I know we have 100Amp breakers in the UK but I am not sure (and cannot definitively find) what the requirement is here in France.
For the house, 36 kVA divided by say 410V (assuming loss from 415) gives a max load of 88 Amps. For the PV feed 15kW divided by 415 V (post inverter) gives 36 Amps.
Below is my software output for the main cable:
50m Length Calculation for Three Phase cable
Any and all advice welcome, TIA,