W

Wardy1980

Hi, I just have a quick question...
in the factory I am working in there is a 63amp Mcb feeding an 32Amp Switchfuse
which is then feeding a little distribution enclosure which has a 20amp Mcb for one
rcd socket, 20amp,16amp, 10amp and a 4 amp for machinery.
is this right because it does not seem right to me?
 
I addressed this with the main electrician on site and he said it is fine as the machines don't pull that much current as he put his clamp meter on each machine and socket outlet and all the current was added up to 26amps
Do does this make it okay?
 
It's a tad poor design ... depends what the machine does too, is he clamping it with a low demand job on it or say it had a motor thats not anywhere near its flc, then the supply, switchgear etc should always be designed for the max demand ... the 32amp isolator should be rated to the front end device if feeding a distribution board especially if it has spare ways.
The fixed load clause seems to have been abused here to excuse a poor design, although I would need more info on loads to say if it contravenes regulations
 
Last edited by a moderator:
With sockets on it then it cannot be classed as a fixed load unless the accumulative values don't exceed the switchgear in this case it is poor design IMHO and only causing no issues due to the way the machine is used and the items plugged in and not by what the machine could demand and what you could plug in.
 
63amp to protect the SWA or whatever feeds the switch fuse
switch fuse somewhere in other part of the building, easy to lock out when the in house spark got some work to do around there.
 
It seems ok to me , Discrimination is fine. the MCB's protect the wiring system ( assuming max demand, diversity and correction factors have all been factored in) Cant see an issue without more details.
 

Reply to Three Phase Distribution Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2 3 4
Replies
47
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top