If the plate says FLC 30amps then its unlikely you can protect this motor with a mcb even if you had it star/delta starting...
If as above you are a Handyman then keep well away from trying to design a motor supply circuit, this is often messed up by experienced Electricians to give you an idea how many factors need to be taken into account when designing a power and starting circuit for a motor - at a guess you have a 15kw motor there and I wouldn't be looking at MCB's as a means of circuit protection or your asking for trouble.
I wire and design motor circuits routinely and depending on how you design it you can happily have a type (b) covering a smaller motor than yours without any issues, this type 'b' for this, type 'c' for this and 'd' for that is a very generalised rule of thumb that gets taught as an introduction in college.
Type 'B' - general use (resistive and light inductive loads)
Type 'C' - moderate inductive loads
Type 'D' - high inductive loads
If a MCB is suitable sized above the load demand and ELI is still met then type 'B''s can be chosen for some motors, this is useful when meeting ELI of a type 'C' or 'D' may be problematic.
I have had this chat with you before, you are well out of your depth Trig, you may question how I know your well out of your depth and how I know what your experience is ... well your profile lists all your threads you start and posts you do, the amount of motor related questions is clearly evident you are getting involved in things you should not be. Getting a motor running running is the easy part, knowing that in various fault scenarios that motor will be protected and the equipment it is used for plus the safety of any user or local persons will not be put at risk is where competence comes in.