shaun gold
I have a three phase dis/board with a measured PFC of 10 kA across each phase (20 kA total) and a Ze of 0.03. The origin is 100 amp BS 1361
type IIb x 3 and the tails are 1.5m long. The MCB's are type B and have a short ciruit rating of 6 kA, should these be changed for 10 kA or higher.
The dis/board is to BS EN 60439-3 and i have checked my results a few times with other (nulled) testers.
The DNO state the three phase supply at 25 kA but this exceeds the permitted 16 kA listed in regulation 434.5.1.
Not really sure what to record on the ECR to tell the client without being 100%.
type IIb x 3 and the tails are 1.5m long. The MCB's are type B and have a short ciruit rating of 6 kA, should these be changed for 10 kA or higher.
The dis/board is to BS EN 60439-3 and i have checked my results a few times with other (nulled) testers.
The DNO state the three phase supply at 25 kA but this exceeds the permitted 16 kA listed in regulation 434.5.1.
Not really sure what to record on the ECR to tell the client without being 100%.