Hi guys, I am rewiring a commercial launderette with 3 phase machinery.



Does the machinery need to be RCD protected being in commando sockets.



The sockets are not accessible to the public and each circuit is being used for a specific machine.



With the price of three phase rcbos the customer is not happy
 
Last edited by a moderator:
Yes, but if the rcbos are cost prohibitive look at the outlets you can fit rcds in (as long as your supply cables dont already need it) probably be similar costs though so hes/shes gotta swallow it, or you cut the plugs off and wire to rotary isolators, also see what manufacturers instructions say
 
3-phase RCBO are expensive and often take up extra space leading to "lost" slots in TPN boards, so you might well end up cheaper to use socket & RCD combinations as @suffolkspark suggests, or as we did for a couple of 3P A/C units to put the RCDs in a DIN box adjacent to the TPN board.

But if the equipment can be hard-wired to lockable isolators for maintenance that would be cheapest and least trouble overall.
 
Don't forget though, there are a few reasons why rcd/rcbo are required, not just because they are socket outlets, so if the wiring is less than 50mm behind the wall etc. Then the rcd function needs to be at the feed end.

Surface wiring or protected cables(armoured or conduit/trunking) would be fine with the rcd at either end.

Surface cable to fixed equipment (no socket) then no rcd required.
 

Reply to Three phase rcd protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

  • Question
<= This The RCD looks at any current imbalance between the cables routed though it, if N is not used then no current so it matters not from a...
Replies
4
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
945

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top