A

adammid

Does anyone know what the min size supply to a building would require its own sub station?
 
Its dependant also on the existing network .... you can require a small KVA but if its a new supply and existing supplies are accounted for then they may require to fit a new sub, as tony already said the only way to answer this is by enquiry to your local DNO.
Ive had over 300kva supplies brought in LV before with no need for seperate sub yet a 150kva request on another site was quoted 60k as they had to fit new sub as the local sub kva allocation was alredy accounted for.
 
Last edited by a moderator:
If its new build like an industrial park i sure there will be guidelines they use but where existing subs' and LV networks exist then its really down to local demand and allocation of KVA with the local existing substations as well as distance from preposed site can also play its part.
 
215KVA is a pretty big supply to be taken off an existing LV distribution network, Maybe if there is a close by DNO sub-station that had sufficient spare capacity to accommodate such a demand you may be lucky. Otherwise and more likely, it will supplied at MV, which i might add if metered at MV is a cheaper unit price than at LV.


Is this supply for an industrial unit, and if so, is it located on an industrial estate??
 

Reply to Three Phase supply Substations in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
695
  • Question
Gents has anyone done an application using the UKPN smart connect portal for a split phase supply and addition of multiple single phase battery...
Replies
0
Views
401

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top