W
waitees
Hi guys
Been out to change some down lighters and gone to the board to find some interesting things.
The supply is three phase and what they have done is convert 3 flats upstairs with single phase as well as the shop.
Each phase is going into a separate meter and as there is only a single neutral they have Henley block this to accommodate for extra neutrals, this does not look right.
Also high pscc of just over 6.5ka for fuses design for 6ka
Any help guys ?