G

GaryM

I'm looking to get my EDF FiT application form completed and have come across Total Installed Capacity and Declared Net Capacity.
My system is comprised of 16 x 250kW panels (4kWp) and a Fronius IG TL 3.6 inverter. My MCS certificate states 4kW for Declared Net Capacity so I assume I put the same for Total Installed Capacity?
i thought the net figure would have been 3.68kW (16A) as the inverter limits the system.
 
Your TIC and DNC should both be specified as 3.68 kW. TIC is the critical figure as it is this that defines which FiT tariff band your system is registered in and hence what rate you get paid. The TIC cannot be less than the DNC but almost all systems that are registered have TIC = DNC.

If your inverter is limited to 3.68 kW then I suggest that your MCS certificate has not been filled out with the correct figure.
 
Probably not, although it could complicate things if you want to extend the array later. If for any reason the DNO decided to cross check their information with the MCS database then if they see you with a DNC of 4kW on the MCS database and you have not had their prior permission then that might raise a hare.
 
Some electricity providers have been known to reject a form if the mcs certificate says a different dnc to their form.
 
Thanks all. No plans to ever increase the size of the array so probably best all round to just enter 4kW for both entries.
 

Reply to TIC and DNC on EDF FiT application form in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I appreciate all that but don't really want to put all the details here in the public domain. If I can identify someone who I can have confidence...
Replies
3
Views
2K
Bury a 4 inch duct under the pathway with drawropes until the time they are needed and pull in the correct size of cable at the time. We would...
Replies
1
Views
719
Hi Sean thanks for the reply. I am getting PE connection missing (9) every few minutes.
Replies
6
Views
3K
Gavin's correct - our independent electro-mechanical failsafe can simply shut down the inverter if the absolute export threshold is breached...
Replies
3
Views
3K
have been reliably informed that the inverter is a dual tracker so the SP2000 should be fine on the system, I will have to have a look on what...
Replies
30
Views
12K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks