B

bobby101

hi all just a quickie


could someone please tell me what the the diffrence is on the tick sheet at 3.6, 3.7and 3.8 i recently submitted a report with these coded a C2 i was was told to choose. At the time i thought it was best to code these all a 2 because it was missing a main earth bond to water please explain what i should do and what to tick many thanks
 
Last edited by a moderator:
What do you mean...you were told to choose? Theres regulations next to the points mate...im not really sure what you're asking here to be perfectly honest.

3.6 is 544.2.1 in the regs.
3.7 is 543.3.2 &544.1.2
3.8 is 543.3.2

but it says this on the EICR inspection schedule anyway. For what its worth, you've got it correct.
 
If a main bonding conductor is missing, then 3.6, nothing more.
If there are main bonding conductors, and you cannot access the connections to the pipework, then 3.7, but you wouldn't tick it just for a missing conductor.
3.8 is really refering to supplementary bonding conductors elswhere in the installation, such as in the bathroom.
 
So if I have an installation where the main bonding conductor is unable to be located I would code 2 the 3.6 box and lim the other boxes
 
No.
If there is a gas bond, but no water, you would place a X in 3.6.
You would then check out the connections for the gas bond, and would either tick or X box 3.7.
Then you would look for the presence of supplementary bonding conductors (6.4) and if present either tick or X box 3.8.

If there is no gas supply, then you would put N/A in box 3.7.

If there is no supplementary bonding, again it would be N/A in box 3.8.
 

Reply to tick sheet query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

It was purely an off the top of my head example, but I'd say - accessible live parts C1 - inaccessible live parts C2 - 10 feet up in a locked room...
Replies
9
Views
723
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top