A small b&b called me about light timer problem, the timer keeps blowing, it is for hallway lights, normally after 5 minutes the lights go off automaticly, but in the last year the times has blown for almost 4 times, so most of the hallway lights are on all the time except some blown ones. i checked the wiring of the timer and all the lights, looks fine, i assume some blown bulbs might have caused short circuit, and i am going to replace all the blown bulbs tomorrow along with the timer, anyone has some experience with this kind of light timer?
 
What type of lighting is it controlling???

Some timers get quite discombobulated once you start using them to switch inductive loads.
 
totally about 10 spot lights, but only 6 are working now, main voltage, i forgot to check the power of the lights, current could be too high actuallybecause the fuse in the timer is only 3A, however the owner said the first timer has worked for 10 years, this only became a problem since last year.
 
Remember filament lamps, especially halogen ones, have a very low resistance when cold.
I assume the 10 lamps are the correct rating... and the timer is of adequate rating for the nominal load.
Someone's not gone along over the years putting 50W lamps in when the originals were 20's have they?

As they are mains voltage, you could replace the failed lamps, and then directly measure the cold load resistance of the circuit.
Calculate the inrush current I=230/ (cold R) (You may be surprised at the result!) and check the timer spec that it is capable of handling such an inrush current.

You may be able to source a timer specifically for halogen lamps that has some sort of slow start - or else use a contactor as southwalesspark suggested.

Simon.
 

Reply to timer is gone again! in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Thanks for the explanation. I did feel the timer getting warm (or even hot), so that could be the cause. I think I'll play it safe and let a...
Replies
10
Views
610
I am a landlord/owner of a flat. I am just about to spur off nearby sockets to provide the additional 24hr supply to new Dimplex Quantum storage...
Replies
0
Views
471
Thank you for your response and interest in helping out on this one. The geyser is rated at 3kW and runs at 220V. To answer the rest of the...
Replies
2
Views
1K
  • Question
Hi Kevin, Thanks for the reply. No I didn't test them individually, as when it tripped a couple of times, I changed the rcbo out for an mcb and...
Replies
5
Views
1K
Probably simpler to put up self contained emergency lights. Either that, or ditch the UPS, use a DC circuit, and run it off a battery that's...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks