aaelectric

Hi All,

Had a job today where the tenant would get a shock from the kitchen sink when she used it.It was not happening all the time.
So i got my meggar out and done and insulation test from all the circuits on the fuseboard to the water pipes. i got a reading of 1.78Mohms. this seems quite low but wouldn be a short on the pipe.bonding is in place as tested to gas 0.03ohm but water is only bonded at the boiler no main bonding.
fuseboard is old rewirable fuses.
what do you think about insulation test and no main bonding on water but at boiler?
Cheers.
 
Thats a low reading, could be a suspected break down of insulation somewhere. Has the customer had any leaks recently in the house?
The main bonding is a big one, it may have supplementry bonding at the boiler, but with no main bonding to connect it to the MET nothing can be bought to the same potential.
 
Could this be the case. there is 2 flats in the building but its not the same landlord and dont no if they are having the same problem

I was being a tad flippant in relation to there being yet another landlord out there neglecting their duties when it comes to electrical safety.

An old board, low IR and limited bonding would suggest at the very least some work needs doing.

Any RCD protection or mains smokes?
 

Reply to tingle from kitchen sink in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
155
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
969
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

M
  • Article
Intermittent bad smell Hi I have an intermittent bad smell that's really hard to pin down, I was wondering if I could get your thoughts on it...
Replies
0
Views
274
MatthewG
M
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top