Hi guys,
Had a strange one yesterday,went to replace a triton shower,straight swop,same unit,
up and running in 20 mins,small leak from shower hose under shower,as nipping it up got a tingle from
hose as my finger touched mains water pipe.tested 240volts between hose and pipe,tested pipe which has continuity to bath
tap.not checked bonding yet.switched power to shower off still 240v,only lost reading when i unscrewed pipe and the
water drained out.shower unit is working ok.even shorted hose and pipe together but 240v still there.
Iknow the reading is not a true 240v but the tingle was real enough.any thoughts?
 
Hi Guys,went back today,tested cable okfound pull switch burnt up and earth loose,
also water pipie not earthed,i am fitting a new switch and an 40amp rcd.
also the water pipe is sunk in wall and is only visible at the shower,with an rcd fitted can i
earth the water pipie from the 6.0mm cpc at the shower?
The earthbonding in the house is ok and there is some plastic water pipes under the bath.
 
hI tel,i suspect the shower has some plastic in it as water pipes near boiler and under sink are bonded,
but as i said under bath is plastic and i think the shower is fed from there.
Can i bond the shower to earth cpc at the shower with rcd fitted?
 
You should always check that both earthing and bonding arrangements are up to current regs before undertaking any work. also to check for supplementary bonding (if required)...... Better safe than sorry mate.........
 
Hi glenspark,The house is unocupied at the moment so had a spare hour so thought i would
fit the shower and have a look round later,i had loaned my meter to a friend on saturday.
much work to do but with no customer can only do shower till they return.
 
Hi glenspark,The house is unocupied at the moment so had a spare hour so thought i would
fit the shower and have a look round later,i had loaned my meter to a friend on saturday.
much work to do but with no customer can only do shower till they return.
No probs mate.....It just seemed strange to me that someone wouldn`t test for CPC continuity and IR and an R2 ....just to cover their own ar$e of course.....
 
You're spot on correct,its just a reminder to myself and anybody reading this the value of testing,
the shower worked ok but a potentially dangerous fault was present.Thank you for your comments.
 

Reply to tingle from shower hose in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

I
  • Article
Not much water from shower head but high pressure in tap Dear Professionals, could you please advise. I have standard mixer tap in my bath (its...
Replies
0
Views
126
IrinaPri
I
S
  • Article
Hissing sound from under sink Heya, So there's a hissing sound coming from underneath my sink that feeds my washing machine and dishwasher...
Replies
0
Views
131
Seo195
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top