Hi guys,

struggling to work this question out and don't seem to be getting a correct answer no matter what cable conductor size i use.

Q. A 230V 14kW domestic electrical cooker, installed in a house is to be supplied by a 15m run of PVC insulated and sheathed cable, clipped to a surface. The cooker control unit has no integral 13A socket. The circuit is to be protected by a BS3036 fuse and the value of external impedance is 0.85 ohms. Calculate the minimum size cable that can be used for this circuit to comply with shock protection.

what ive tried so far:

Ib = 14/230*1000 = 60.87A
In = 100A therefore max Zs = 0.53 ohms. ( i think)

Zs = Ze + [(R1+R2)*mf*L]/1000

Zs = 0.85 + [(1.83)*15] / 1000

Zs = 0.88 ohms ( too high)

using 50mm cable Zs = 0.85 + [0.387*15] / 1000

Zs = 0.86 ohms (still too high)

Feel im missing something obvious.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
TMA question, stuck. please help.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
atto2007,
Last reply from
spark 68,
Replies
6
Views
5,001

Advert

TrueNAS JBOD Storage Server

Back
Top