Hi. Can any one clear some thing up with my schedule of test results for form? The situation is this. I'm testing a building with TN-C-S coming into the switch room. The earthing arrangement being used for the DB's coming out of the main switch gear is TN-S. When filling out the schedule of test result form, do I tick TN-C-S for the main system or TN-S for the earthing arrangement?
 
It's TNC-S it cannot possibly change, it is combined up until the in comer but then seperates from there, that is the definition ofTNC-s!!, it's not possible for the arrangement to change.

Don't forget your arrangent is relevant to your ZE, however post switch room it becomes ZDB and simply forms part of the R1&R2 part of your earth fault loop path .
 
Hi. Can any one clear some thing up with my schedule of test results for form? The situation is this. I'm testing a building with TN-C-S coming into the switch room. The earthing arrangement being used for the DB's coming out of the main switch gear is TN-S. When filling out the schedule of test result form, do I tick TN-C-S for the main system or TN-S for the earthing arrangement?

As PME/TNC-S provides you with (for want of a better word) an ''artificial'' earthing point, that earthing arrangement will remain the same throughout the installation as a whole. The N-E connection will only be present at the at the DNO's incoming service head.

Now, is your supply to the Main Switch room coming from an on-site MV/LV distribution TX?? If it is, then you will probably looking at a TN-S earthing arrangement. What you could be looking at within the Main Switchboard, is the TX neutral earthing point!! It can get a little confusing for those that don't have larger project experience... lol!!
 
Hi Toni mc. I know the main switch gear and the local energy supplier have installed TN-C-S. But when the DB's are supplied with an armour cable with the armour being the earthing conductor, does this now make the DB's TN-C or is the whole system TN-C-S? ie switch room and DB's installed into the system.
 

Reply to TN-C or TN-C-S in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
290
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
276
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K
N
  • Question
In my first sparking era (late 90's) I was always told to run a neutral to the isolator, as the chances are whoever is using the machine will...
    • Like
2
Replies
21
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top