Hi just wondered what the rule of thumb is for calculating the main protective conductor is in a tn-c-s system as l have a supply with 185mm cables and a 50mm main earth?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss tn-c-s earthing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi just wondered what the rule of thumb is for calculating the main protective conductor is in a tn-c-s system as l have a supply with 185mm cables and a 50mm main earth?
Amtech Pro
50mm² should be fine.Hi just wondered what the rule of thumb is for calculating the main protective conductor is in a tn-c-s system as l have a supply with 185mm cables and a 50mm main earth?
To be fair your probably right.
I have not had the pleasure (or the bank balance) to be able to utilise the software.......I believe you would always cross check the calculations for the sake of accuracy though.
no its a 400A supply
I imagine with that PFC, you would be looking at a disconnection time around 0.1s, which would give a CSA for the CPC of about 20mm².8.9KA and protective device l think is a BS 88