I have been asked to provide a supply to 2 x containers on a contruction site (1 for materials 1 for tea hut) with sockets for battery chargers etc. The supply at the house to be refurbed/extended is TN-C-S.

Reg 704.411.3.1 prohibits use of TN-C-S unless to a fixed building.

Could these containers, which will not be moved for the duration of the contruction be considered fixed?
 
yes 2 core cable ..

at the container end..

if its SWA your using then you have to terminate the SWA into a plastic enclosure with an insulating compression gland ( not a standard SWA gland ) and insulating tape to insulate the armor. this is to completely isolate the the cabins from the origin ( and any faults that may appear at the origin and be passed along the armor creating a shock hazard ) connect new earth rod near cabins. obviously the SWA will be earthed as normal at the origin. this also applies to agricutural supplys for new barns etc.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
TN-C-S supply to contruction site
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
knight1,
Last reply from
The Truth,
Replies
4
Views
1,251

Advert

Back
Top