Hello!

Where do I start to troubleshooting with issue of higher reading of Ze 0.45ohms with TN-C-S earthing arrangement. Thank you!
 
Is it an issue for your Zs readings? You could ask your DNO, but I think they might say in was within acceptable limits, unless there's something nasty looking in the earthing facility.
 
Worth carrying out a test L-N and seeing if the reading is the same. Some service heads have a link fitted between the earth block and N block. On two occasions I have recorded a high Zs reading but the L-N reading was much lower. Turns out the link was missing and the high reading was via the only earth path through main bonding.
 
Worth carrying out a test L-N and seeing if the reading is the same. Some service heads have a link fitted between the earth block and N block. On two occasions I have recorded a high Zs reading but the L-N reading was much lower. Turns out the link was missing and the high reading was via the only earth path through main bonding.
Thank you! I will try this test.
 

Reply to TN-C-S with Ze higher than 0.35 ohms in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K
N
  • Question
In my first sparking era (late 90's) I was always told to run a neutral to the isolator, as the chances are whoever is using the machine will...
    • Like
2
Replies
21
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top