G

Gamma

Hello all.
According to BS 7671, (411.4.4 Note 1), on TN C systems it is prohibited to use RCD protection.Could someone please explain why???
Background info is: Small industrial unit supplied by a TN C system. DB then splits to supply a set of offices and toilets via a 6 way domestic CU. Client wants to upgrade to a 17th edition RCD protected unit. Would this present a problem ?
 
With TN-C the earth is combined with the neutral, This means that an RCD will have no way of seeing the inbalance between earth/ Neutral should a fault develope.

TN-C is a rare combination these days so check it really is that kind of earthing arrangement.
 
Gamm to tell the difference you have to find where the neutral and earth split. Is it before or after the meter?

If its before its a TN-C-S if its after at the Main D.B ther will be a Link betwenn Phase and Neutral. TN-C
 
Lister TNC systyems have to be "Under supervision of a competent person" so you dont have to use RCDs . They are also thankfully very rare.

Have a look at 411.4.1 its pritty clearly worded that no rcds on a tnc system.

In that system its down to the sparks to ensure the ZS is low enouph for disconnection times by either supplimentary earthing, use of overcurrent devices. for example HRC fuses instead of MCBs you have to be VERY CAREFULL.

I would try and change the earthing system to TN-C-S myself if possible.
 
Thank all that have responded to my dilemma, I havnt checked the system myself, but client produced an 11 year old EIC which clearly stated system type : TN C. I will drop by today and look for myself and post result tonight.:(
 
Update as promised: The TN C system turned out to be TN C S so no probs with the RCDs. Thanks again to all who responded.:)
 
To add to this.. I think i may have come across a TN C system. Would like some advice is possible. After taking a peek in the meter cabinet i noticed a strange layout that i cant say ive seen b4. This had a yellow sticker on saying "WARNING This installation is connected to a network with protective multiple earthing Please consult YEB regarding earthing?. Have some pictures but will need to upload from my mobile when i get the chance..
 
Last edited by a moderator:
Agreed, sounds like it's a TN-C-S (PME).

It is very rare to come across a TN-C system particularly in a domestic situation for the simple reason that you cannot use RCD's.
 
muikeymoo PME is also known as TN-C-S lets see the photos to prove it though

Isnt TN C also known as PME? Will upload pics.
The installation is approx 28 years old if thats a clue. When would you normaly find a TN C system? Was it used just to reduce the risk of broken neutrals?
 
Last edited by a moderator:
Thanks for the link mate.. From info, if i were to take alook inside the cu and the earth and neutal are seperate then its TN-C-S? because in TN-C system its combined throughout??


Just phoned YEDL tec helpline and can you believe it they dont hold info regarding the earthing arrangments!!. And wanna relieve me of £150 to come fit an earthing block. Also to add insult to injury will take 6-8 weeks!!. Whats the crack with me adding the earthing block myself?? Will get around to unloading those pics today so if someone could take a look i would be grateful.
 
Last edited by a moderator:
If you look at page 32 of the big red book you are NOT allowed to use a TN-C as a consumer under ESQCR Regulations 2002.

The DNO can supply you via this way but then it must split at the point of intake giving the cosumer a seperate earth and neutral.
 

Reply to TN C system. RCD ??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
503
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
975
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
3K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top