Evening gents,
I'm just looking for some guidance/clarification on a supply to a summer house I installed. I had to put in a small CU (the existing one had no spare ways left) with a 63A 30mA RCD main switch and a 45A B type feeding the distribution circuit. 6mm2 2 core SWA around a 25m run to the summer house that fed a garage CU with 40A 30mA RCD main switch.
The small CU I put in the house had a Ze of 0.2 ohms and the Distribution circuit had R1 +R2 of 0.33 ohms. The Zs of the circuit/Ze of the garage CU was 0.79 ohms.
Now looking at table B6 in the OSG shows that max measured Zs for 45A b type is 0.82 but I wasnt sure if that includes distribution circuits. Reg 411.3.2.3 states that for a distribution circuit a disconnection time not exceeding 5 seconds is permitted and 411.4.5 says: Zs x Ia < U0
Am I right in thinking that 0.79 x 225A = 177.8 so that it complies?
Apologies in advance for the wall of text and as you might of gathered I'm fairly new to this!
Thanks for your time
Matt
I'm just looking for some guidance/clarification on a supply to a summer house I installed. I had to put in a small CU (the existing one had no spare ways left) with a 63A 30mA RCD main switch and a 45A B type feeding the distribution circuit. 6mm2 2 core SWA around a 25m run to the summer house that fed a garage CU with 40A 30mA RCD main switch.
The small CU I put in the house had a Ze of 0.2 ohms and the Distribution circuit had R1 +R2 of 0.33 ohms. The Zs of the circuit/Ze of the garage CU was 0.79 ohms.
Now looking at table B6 in the OSG shows that max measured Zs for 45A b type is 0.82 but I wasnt sure if that includes distribution circuits. Reg 411.3.2.3 states that for a distribution circuit a disconnection time not exceeding 5 seconds is permitted and 411.4.5 says: Zs x Ia < U0
Am I right in thinking that 0.79 x 225A = 177.8 so that it complies?
Apologies in advance for the wall of text and as you might of gathered I'm fairly new to this!
Thanks for your time
Matt