Hi,
I undertsand this to be a TN-S system as the earthing arrangement comes along the SWA metal sheath surround but the Ze i got is 0.19 which falls out side the regs of 0.8.
Chameleon Electrical - https://www.facebook.com/Chameleonelectrical/photos/a.162578514404078/251251892203406/?type=3&theater

I have also read on here that if the earth is then connected to an earthing block as shown on picture, it then becomes a TN-C-S! which doesnt make sense as the earth is outside the sheath not inside on the neutral!

Which is it?
 
That appears to be a loop through TNS supply.

The earthing block to which you refer is the main earth terminal for the installation. This can be a separate entity, as it is in your photo, or the earth terminal bar in the consumer unit.

The main earth clearly comes off the sheath of the cable (this is what makes it TNS) into the main earth terminal. If it was TNCS, the earth block would be on the other side (the neutral side) of the service head, usually with the main earth leaving the service head on the same side.

As for the Ze... 0.8 is the maximum recommended I believe (i.e. if it's more, give the DNO a call). 0.19 is much lower and so it's a fine example of a good earth. No problem there.
 
0.19 is better than 0.80, so good there, however in answer to the question I would say it is TNS
 
If you are unsure if its a TNS or a TNCS system by looking at it ( ie not sure if its been upgraded to TNCS ) You could do a simple continuity test between the neutral & earth at the mains switch to confirm this.

That won’t necessarily help as N and E are still linked at the substation for TNS so there is continuity between them in both systems.
Comparing the measured resistance may help, but it’s not guaranteed.
 

Reply to TN-S or TN-C-S From this photo in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top