Whilst having a quick nosy at my mum's supply I came across a recent installation certificate that was left when her new central heating system was fitted. Before reading the certificate, I was of the opinion it was a TN-C-S supply. However, according to the certificate, they noted it as a TN-S supply with A Ze of 0.22. So I thought I'd stick a few photo's up and see what you guys think as I'm now a tad confused :confused:
 

Attachments

  • [ElectriciansForums.net] TN-S or TN-C-S?
    SP_A0768.jpg
    93 KB · Views: 114
  • [ElectriciansForums.net] TN-S or TN-C-S?
    SP_A0767.jpg
    90.8 KB · Views: 101
  • [ElectriciansForums.net] TN-S or TN-C-S?
    SP_A0758.jpg
    154 KB · Views: 112
apart from being RAF, how is the main earth connected. ? TN-S is on the incoming metallic sheath of the supply cable. TNC-S is linked to the neutral in the cut-out.

edit. looks like the thin bare wire to the metal box is the main earth. does that box house the DNO fuse? if so, it looks like TN-S
 
Last edited:
Very difficult to tell, was it a TT system previously?

If so then it's likely to be a TN-C-S try an earth loop and neutral loop and see if the results are the same, that will almost confirm TN-C-S.
 
it,s a tns supply, the supply cable is the pyro and the earth to the earth terminal block is coming from the casing of the housing, I would also add that it could do with an upgrade,

does the supply come from a pole mounted transformer
 
it,s a tns supply, the supply cable is the pyro and the earth to the earth terminal block is coming from the casing of the housing, I would also add that it could do with an upgrade,]
that's just what i thought. upgrade to current type head
 
Is this a flat Manda ? As I would say that your riser cable is MICC/Pyro, as that looks to me to be a pyro terminating into that white header box, which as a seal on it, and most likely as a BS 1361 fuse inside it.

You also seem to have an upfront RCD from the meter before it goes into the CU, so I dont think it will be a TNC-S. From that white header box you look to have a really small 1.5mm earth to the BMT, which should be changed as its unprotected and not mechanically protected.

Now becasue you have an RCD there, by the way what size is it 100mA or 30mA, as you also seem to have an RCD in the CU. I think what as happened , the house will have a TN-S supply and they may not be able to achieve good Zs results on the final circuits and so fitted an upfront RCD providing protection.

Now if you mums is a flat you will have to find where that Ze was taken, was it at the origin where it should be, or was it at your mums board where it would be a Zdb. If it was at your mums board and it is a flat then that 0.22 is quite easily got due to parallel paths, can you give us a little more info as I might be well out lol
 
There is no earth to the metalic cable, at least not on the outside of the cut out. It is sealed and I don't fancy breaking the seal just to nosy. As for testing it, there is soon to be some work done, so I'll get it tested then out of interest. I don't know if it was previously a TT system, she's only been in there 5 years so all I can say is not in that time. Just wondered if I was missing something that was visually obvious without breaking the seal. Also, would a Ze of 0.22 be acceptable for TN-S as I thought the Maximum was 0.8 thus making it more likely to be a TN-C_S?
 
You also seem to have an upfront RCD from the meter before it goes into the CU, so I dont think it will be a TNC-S. From that white header box you look to have a really small 1.5mm earth to the BMT, which should be changed as its unprotected and not mechanically protected.

Now becasue you have an RCD there, by the way what size is it 100mA or 30mA, as you also seem to have an RCD in the CU.

There's no RCD in the CU, so the upfront RCD was probably just installed to provide RCD protection rather than anything to do with Zs
 
Yes it's a flat in sunny Rochdale. I was also a little perplexed at the lovely unsheathed earth wire. Not a clue where the readings were taken as I wasn't there when they installed it. The RCD is 30mA if I remember right, I'm home again now so can't check, but pretty sure it was 30mA.
 

Reply to TN-S or TN-C-S? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K
  • Question
How did it go?
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top