TN-S vs TNC-S (PNB) Earthing System | on ElectriciansForums

Discuss TN-S vs TNC-S (PNB) Earthing System in the Talk Electrician area at ElectriciansForums.net

Andy-1960

-
Arms
Joined
Feb 20, 2017
Messages
572
Reaction score
612
Location
Wolverhampton
What are the thoughts of you guys on the differences between a TN-S and a TNC-S (PNB) Earthing System.

My understanding is as follows:

TNC-S (PNB) - the Neutral & Earth Conductor are joined in the main switchboard with the neutral conductor between the transformer and the switchboard then being the earth fault path back to the transformer star point.

TN-S -a separate earth conductor is installed between the transformer and the switchboard and the neutral and earth are joined in the transformer cable box, the earth fault path back to the transformer start point.

So, depending on your thoughts, would you then say the source of supply is the switchboard or the transformer... I know what I think, but I have a customer who disagrees.
 
This has been chewed over many a time. Some argue the neutral from the transformer star point to the customers panel does not have a combined function, it is merely moving the star point to the panel where the earth is taken from so at this point it is TN-S. Others argue the reverse that the neutral does have a combined PEN function and is not shifting the star point from the transformer hence PNB.
 
PNB is TNS. It cannot be TNC-S as there is no conductor that shares the "earth" and "neutral" functions. It also cannot be "PME" as there is only a single connection to earth. PNB is used where a transformer supplies a single large customer. The earth reference for the transformer star-point is made at the customer's end of the supply cable, as there will not usually be a fuse rack in the DNO's substation.
 
In the UK, it’s very rare to find a link between neutral and earth within the customer’s installation.
PNB as Buzz says is more akin to TN-S as it uses separate conductors. However it is treated in the UK as being TN-C-S.

It’s not correct to say there is only one connection to earth.
It will depend on the distance between the transformer and the installation.
Could be just the one electrode and link somewhere between, or there could be two, one close to the transformer and the other close to the installation.
 
PNB is TNS. It cannot be TNC-S as there is no conductor that shares the "earth" and "neutral" functions. It also cannot be "PME" as there is only a single connection to earth. PNB is used where a transformer supplies a single large customer. The earth reference for the transformer star-point is made at the customer's end of the supply cable, as there will not usually be a fuse rack in the DNO's substation.
christ buzz, you been eating dictionaries?
 
christ buzz, you been eating dictionaries
[ElectriciansForums.net] TN-S vs TNC-S (PNB) Earthing System
yep.
 
A TN-S will have a single earth conductor from the star point of the DNO transformer.

As in ‘S’ - seperate

A TN-C-S is combined on the DNO side ‘C’ and seperate on the installation side ‘S’.

A PME will be earthed at multiple points along the PEN conductor and then linked out at the termination within the installation.

A PNB will only be linked out at the installation with no other earthing points. As soon as another earthing point is put in along the PEN conductor it ceases to be a PNB.
 

Reply to TN-S vs TNC-S (PNB) Earthing System in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
657
N
  • Question
In my first sparking era (late 90's) I was always told to run a neutral to the isolator, as the chances are whoever is using the machine will...
    • Like
2
Replies
21
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top