Tn system | on ElectriciansForums
Discuss Tn system in the Australia area at ElectriciansForums.net
G
gordy
Ok. If my overcurrent protective device has a max zs of 1.20ohms and my measured zs is 1.30ohms in a tn installation. I know this is unsatisfactory as it will not meet disconection time permitted.
So if i replace my overcurrent protective device with and rcbo? Is this acceptable by bs7671?
Cheers
Gordy
I think before just buging in an RCD/RCBO I'd check to see if there there was anything wrong first by checking the circuit constraints to see if they added up correctly with R1+R2 & Ze etc. If it is sound then fit the additional earth fault protection.
Obviously if it is a new circuit, a good design would have picked this up and a larger cable could have been selected, as the circuit may not neccessarily have needed RCD protection otherwise and could become a nuisance.
Reply to Tn system in the Australia area at ElectriciansForums.net
Hey Tim, Thank you so much for taking the time to explain this, that has really helped clarify the matter for me.
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...