Hi. New to the forum. I hope I've chosen the correct category to place my post.
I tested a landlords property recently, turned out to be TNC. I haven't much experience encountering TNC systems. So I've signed up here to pick a few brains.
I'm filling out the report now and keep stumbling on parts due to this type of earthing system.
Bit of info on the property:
Cable enters property into cut-out (60amp) 16mm^2 tails from cut-out to meter, 16mm^2 tails from meter to CU. (No earth as TNC. Do I record the Earthing conductor as 16mm^2?)
Old Wylex board BS5486. Once used re-wireable fuses but now has BS3871 in place.
I then have a 6mm^2 bonding conductor from the Earth-bar in the CU to the Water/Gas
When testing I performed a Zs at the CU., My result 16.3 ohms
I also performed a Zline test at the CU. My result 0.22 ohms & 1.04Ka
Obviously my readings for the Zs are not compliant. I'm questioning myself if I've done it right and how you would test & record the results from a TNC? or would you take the Z Line result? but that's a different test measuring the PFC.
The property also had no supplementary bonding in place, would I be right in thinking due to the system type that it's quite significant? (eg. Code C2)
I'm sure I have more questions to come...
Thanks
I tested a landlords property recently, turned out to be TNC. I haven't much experience encountering TNC systems. So I've signed up here to pick a few brains.
I'm filling out the report now and keep stumbling on parts due to this type of earthing system.
Bit of info on the property:
Cable enters property into cut-out (60amp) 16mm^2 tails from cut-out to meter, 16mm^2 tails from meter to CU. (No earth as TNC. Do I record the Earthing conductor as 16mm^2?)
Old Wylex board BS5486. Once used re-wireable fuses but now has BS3871 in place.
I then have a 6mm^2 bonding conductor from the Earth-bar in the CU to the Water/Gas
When testing I performed a Zs at the CU., My result 16.3 ohms
I also performed a Zline test at the CU. My result 0.22 ohms & 1.04Ka
Obviously my readings for the Zs are not compliant. I'm questioning myself if I've done it right and how you would test & record the results from a TNC? or would you take the Z Line result? but that's a different test measuring the PFC.
The property also had no supplementary bonding in place, would I be right in thinking due to the system type that it's quite significant? (eg. Code C2)
I'm sure I have more questions to come...
Thanks