Ok, I'm leaving myself open for some serious abuse here.... I was asked a question today, who can answer it.

question: how do you identify a tncs system through testing at the consumer unit when you have no access to the incoming head? So what they are asking is how do you determine what the incoming supply is, tns or tncs
 
Check the PSCC and PEFC, on a TNC-S system they will be exactly the same. (for Single phase).

On 3-phase check ZP-N and Ze again they will be substantially the same.
 
Last edited:
Ok, I'm leaving myself open for some serious abuse here.... I was asked a question today, who can answer it.

question: how do you identify a tncs system through testing at the consumer unit when you have no access to the incoming head? So what they are asking is how do you determine what the incoming supply is, tns or tncs

Asking a question like that (or any other question) shouldn't leave you open to abuse. Its a fair question, and i bet there are plenty of people who didn't know.

Cheers…………Howard
 
Thanks Howard.

My answer is actually badly worded, I should have said compare Ze and Z P-N for both SP and TP+N, as with all bonding connected in taking the PEFC reading, this could give a slightly higher reading compared to the PSSC in some circumstances.

I knew what I meant though, lol.
 
Ok, I'm leaving myself open for some serious abuse here.... I was asked a question today, who can answer it.

question: how do you identify a tncs system through testing at the consumer unit when you have no access to the incoming head? So what they are asking is how do you determine what the incoming supply is, tns or tncs

Never identify anything without seeing it first. If there's no access to the service head, then don't do the job.
 
Never identify anything without seeing it first. If there's no access to the service head, then don't do the job.

Agreed. Results should confirm what your eyes tell you.

Then again.......could be a bit of a problem if working on a final sub circuit at Heathrow airport.
 

Reply to Tnc-s in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
926

Similar threads

I am with you. Their RCD did not comply with the standard. The only one I know that does comply, though I am sure it isn't alone, is the Garo...
    • Like
Replies
10
Views
771
Thanks for the advice, I actually had no idea about the HMO licensing rules so have learnt a lot. Just did a search, its not licensed as an HMO...
Replies
5
Views
463

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top