Was reading the spring 'Connections' mag today. In the 'questions' section the query was is it ok to carry out an alteration or addition to a TNCS install if the bonding is in 6.0mm and not practical to upgrade.
The answer was a definite no, it must be upgraded to 10.0mm. The article even suggested a way round this would be to convert to TT! Of course in the vast majority of situations we would all upgrade....
But I always thought the guidance on this was that if it really is not practical to upgrade, that if the 6.0mm has been in place for some time,and there is no sign of thermal or other damage, then a competent and qualified person can make the decision that the existing bonding is adequate.
Now I have not upgraded on very few occasions, but took our NICEIC assessor to a DB change where the 6.0mm remained in place on his last visit,and he was quite happy that there was good reason to leave it in place.
Another scenario may be with perfectly fine 6.0mm bonding in place...and just an additional socket to be added. That is hardly going to affect existing bonding arrangements or change anything.
'No madam, the bonding has been absolutely fine for 20 years,but because of that new socket you want You'll have to spend ÂŁ200 putting a slightly bigger bonding wire in, but first you'll have to take up all that oak flooring you've just had laid on the landing, that OK?'
Has something changed or is that Connections article boll****?
The answer was a definite no, it must be upgraded to 10.0mm. The article even suggested a way round this would be to convert to TT! Of course in the vast majority of situations we would all upgrade....
But I always thought the guidance on this was that if it really is not practical to upgrade, that if the 6.0mm has been in place for some time,and there is no sign of thermal or other damage, then a competent and qualified person can make the decision that the existing bonding is adequate.
Now I have not upgraded on very few occasions, but took our NICEIC assessor to a DB change where the 6.0mm remained in place on his last visit,and he was quite happy that there was good reason to leave it in place.
Another scenario may be with perfectly fine 6.0mm bonding in place...and just an additional socket to be added. That is hardly going to affect existing bonding arrangements or change anything.
'No madam, the bonding has been absolutely fine for 20 years,but because of that new socket you want You'll have to spend ÂŁ200 putting a slightly bigger bonding wire in, but first you'll have to take up all that oak flooring you've just had laid on the landing, that OK?'
Has something changed or is that Connections article boll****?