Went to do a small addition on a construction site last week. The installation was installed and certed by others 6 months ago and consists of 3 transportable units (converted steel containers). They are fed by an SWA from a TNCS supply to a junction box,this then feeds the 3 units via 3x32a plugs into 32a inlet sockets on the outside wall of the units. Now bs 7671 prohibits the use of TNCS on a construction site except for fixed buildings,and section 717 prohibits it's use for transportable units unless under the supervision of an instructed person and the suitability of the means of earthing is confirmed before connection.
Firstly is a transportable administative building classed as 'fixed' for compliance with section 704 (construction sites).....and secondly is a recommended retest interval classed as 'under supervision of an instructed person' for compliance with 717...(transportable units) ?

This seems a grey area,I noted the TNCS supply on my MW cert for the job,and stated that it was assumed that the original installer had assessed the suitability of a TNCS supply at the time the EIC was provided. However I'm now wondering whether I should have flagged this up before carrying out any work.
Your thoughts please esteemed members.
 
Getting late, tired. Worked for a DNO and anything that was "portable" like porta cabins etc, PME would not be provided. The same with any steel enclosures even thought fixed, PME would not be provided.
 
I wouldn't class it as fixed, personally, being fed via 32amp inlet sockets and plugs. I'd go with the recommended (717) as a result.

However, if the condition of the installation is good, I wouldn't worry, it being extremely unlikely that problems will ensue and having only carried out a MW. Grey area, I agree, but you've stated your asumption re the original installer.
 
If it is a building site then TNS or TT is acceptable to the sockets, remember as it is a building site it will want a EICR carried out and a copy of the report handed to the site manager/foreman every 3 months, PME/TNCS is an absolute no-no on a construction site for temporary buildings, I would drop the earth off into a wago or connector at the sockets and drive a 5ft rod in to the ground under the sockets and TT them there.
 
If it is a building site then TNS or TT is acceptable to the sockets, remember as it is a building site it will want a EICR carried out and a copy of the report handed to the site manager/foreman every 3 months, PME/TNCS is an absolute no-no on a construction site for temporary buildings, I would drop the earth off into a wago or connector at the sockets and drive a 5ft rod in to the ground under the sockets and TT them there.

Agreed but I think Wirepuller knows the score. He's only done a small addition and made his thoughts and observations known.
 
Should really be flagged before hand. Same category as main bonding for any prework survey ie suitability and provision of earthing system. Talk to the site super and ask if he wants it sorted? Any provision for lightning protection?
 
Went to do a small addition on a construction site last week. The installation was installed and certed by others 6 months ago and consists of 3 transportable units (converted steel containers). They are fed by an SWA from a TNCS supply to a junction box,this then feeds the 3 units via 3x32a plugs into 32a inlet sockets on the outside wall of the units. Now bs 7671 prohibits the use of TNCS on a construction site except for fixed buildings,and section 717 prohibits it's use for transportable units unless under the supervision of an instructed person and the suitability of the means of earthing is confirmed before connection.
Firstly is a transportable administative building classed as 'fixed' for compliance with section 704 (construction sites).....and secondly is a recommended retest interval classed as 'under supervision of an instructed person' for compliance with 717...(transportable units) ?

This seems a grey area,I noted the TNCS supply on my MW cert for the job,and stated that it was assumed that the original installer had assessed the suitability of a TNCS supply at the time the EIC was provided. However I'm now wondering whether I should have flagged this up before carrying out any work.
Your thoughts please esteemed members.


You need to work to the general requirements of BS7671 and section 704 in conjunction with BS7375. Now its clear that canteens, toilets and administrative units fall outside of 704, so general requirements apply.

Chris
 
If it is a building site then TNS or TT is acceptable to the sockets, remember as it is a building site it will want a EICR carried out and a copy of the report handed to the site manager/foreman every 3 months, PME/TNCS is an absolute no-no on a construction site for temporary buildings, I would drop the earth off into a wago or connector at the sockets and drive a 5ft rod in to the ground under the sockets and TT them there.
According to section 704 TNCS is allowable to fixed buildings on a construction site,so the question really is whether a transportable unit which is going nowhere for the duration of the site work meets this requirement

He is very knowlegable without doubt, however he dropped a clanger on this occassion, he shouldn't have done any work under those circumstances.
Again...the area of concern is administrative,if you read through section 704 and 717 there is no cast iron TNCS not permitted regulation,it is open to interpretation. I may have dropped a clanger...or I may not. But certainly if I was doing the original install I would not have used the TNCS earth system.

You need to work to the general requirements of BS7671 and section 704 in conjunction with BS7375. Now its clear that canteens, toilets and administrative units fall outside of 704, so general requirements apply.

Chris

Indeed,possibly.....but that still leaves section 717.

Thanks for all the replies guys....much appreciated. I still feel by noting it on the MW cert I completed and stating that the responsibility for assessing the suitability of that means of earthing lies with the original installer I have covered my ---....(hopefully)
 
According to section 704 TNCS is allowable to fixed buildings on a construction site,so the question really is whether a transportable unit which is going nowhere for the duration of the site work meets this requirement


Again...the area of concern is administrative,if you read through section 704 and 717 there is no cast iron TNCS not permitted regulation,it is open to interpretation. I may have dropped a clanger...or I may not. But certainly if I was doing the original install I would not have used the TNCS earth system.



Indeed,possibly.....but that still leaves section 717.

Thanks for all the replies guys....much appreciated. I still feel by noting it on the MW cert I completed and stating that the responsibility for assessing the suitability of that means of earthing lies with the original installer I have covered my ---....(hopefully)

717 isn't really appropriate with regards construction site, there are subtle differences. These issues are dealt with within 704 and BS7375.

Chris
 
Slightly if topic

There used to be a guidance on the industry section , on the electrical safety website , that if mobile or transportable units were connected by swa. They were no longer classes as mobile or transportable and general rules applied.

Like that made it any safer :-/
 

Reply to TNCS construction site transportable unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
664
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top