Hi All,
As mentioned, I’ve got what looks like a TNCS system but CPC is coming via an earth rod???? Not tested TNCS system yet to see if earthing is acceptable
 
There is nothing to stop anyone adding earth rods to a TNCS system. Amendment 2 mentions this.
The real questions are probably:
-is it TNCS system?
-does the earth rod have a specialist purpose that needs to be understood?
Feel free to stick some photos up.
(Obviously, measuring what you think is the external loop impedance from the supplier, as well as the L-N loop impedance would help.)
 
They could have got there by many different means: it could have been TT and DNO now converted to TN-C-S, or it could still be TT if there was reason(s) to want to avoid the supplier's earth (for example, it feeds extensive outdoor metalwork, areas where PME is prohibited, etc).

As @timhoward says there is no harm, and often a small advantage, in adding rods to the supply earth, so if it simply is that situation then nothing really needs changing.
 
What type of installation is it? In certain circumstances such as temporary supplies to building sites the DNO can put in a TNCS supply but with hold the earth connection so that the site has to TT it.
 
Hi All,
As mentioned, I’ve got what looks like a TNCS system but CPC is coming via an earth rod???? Not tested TNCS system yet to see if earthing is acceptable
CPC or Main Earth?
 

Reply to TNCS CPC not used in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
710
totally agree
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top