hi guys just a question on tncs

TNCS has a combined earth / neutral

am i right in saying If the neutral failed then the whole installation would become live and you would also loose the earth, however if you bonded the incoming services (water/gas) would this become the fault path? through the met, down the bonded pipework, through general mass of earth and back to the transformer like a tt system ??
 
Yes if the neutral was lost you also lose the earth.
If there is a line fault to earth and the resistance through the pipe work is less than 1667 ohms then any 30 mA rcd will still trip.
 
Last edited by a moderator:
Depends where the neutral is lost. PME = Multiple earthing.. ie lots of earth rods along its path. Infact on the new installs I have seen (industrial) they always plonk a rod in whilst they are onsite. and so even if the neutral failed just outside, you still have an earth path
 
Last edited by a moderator:

Reply to TNCS earthing arrangent in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

Thank you, I had not considered the higher current in the good PEN, I must look as the building I work in has 3 or 4 supplies, there were separate...
Replies
3
Views
878
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top