Discuss tncs ze 12 ohms? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

swift_2

Hello people I was wondering if you could help me understand how a tncs ze value be 12 ohms. All breakers off main conductor disconnected and two lead test with megger 1553 between line and earth tester set on high as no trip not needed. Reading is 12 ohms,so to check this again I left earth disconnected at board and took reading with earth probe on the neutral/earth block. The weird thing is all zs readings complied with regs, there is no earth on the water so surely the readings cant just be complying due to the gas equiptional bonding? Any thoughts would be appreciated. Thank u in advance
 
I know it sounds daft but have you checked the termination screws are tight in the earth-neutral block? Is it 16mm earthing? I have heard of cable made god nows whare mascerading as copper but infact its alli with a copper coating.........Your Zs may comply due to parallel resistances bringing the true Zs down......
 
Last edited by a moderator:
get DNO out to sort it. Ring the emergency number and they will be out in less than 4 hours. You cant leave a job like that can you ??
 
measure your PSSCand PEFC. they should be virtually identical. if not, then you have a fault with the PME.
 
i've had this a couple of times before, had a reading of 23 ohm today in a flat, work it back to the mains, this was due to a loose neutral in the DNO's isolator, tighten up and and away i go, if i remember right that is exactly the same fault as before.
 
GLENNSPARK, The termination was tight, could be that type of cable !

Blowcat, The Ze at the neutral earth point was 12.0 while croc clip around conductor was 12.1.

Mechelec - It wasnt my job, a friend of mine had asked me to look at the house as he was thinking of buying it, nobody living there.
The scary thing is the owner had had it inspected in 2007 where this had been mentioned in the report I seen the other day. In the schedule of test results all Zs readings were measured high, Im thinking the Inspector used the calcuated method. Apparently the owner was a diy guy and has wired the house himself !
Telectrix, PFC and PSSC were identical 2.4 Ka
Didnt think of the loose connection on DNO side of neutral, that could be the cause.
 
Last edited by a moderator:

Reply to tncs ze 12 ohms? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

Similar threads

Hi Dave thanks for the info I revisited the premises to change a cooker switch and redone the test from the MET with MET disconnected from DB...
Replies
16
Views
1K
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
696

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top