But they might compromise at 2x DB next to each other if it avoids then having the RCD they obviously don't want

But the switch fuse will still be at the origin of the installation and this is where the problem is, the final DB MCB's shouldn't have a problem with the Zs values being quoted above...
 
But the switch fuse will still be at the origin of the installation and this is where the problem is, the final DB MCB's shouldn't have a problem with the Zs values being quoted above...

But with 2xDB at the far end he could run 2x smaller sub mains which might have a more achieveable max Zs
 
Were now getting into the realms of over design just to try and cater for a higher than expected Zs. So now you'll need a suitably sized front end isolator switch, rated at say 300A, Two suitably sized switch fuses rated at say 125/150A, and two suitably sized DB's......
 
Were now getting into the realms of over design just to try and cater for a higher than expected Zs. So now you'll need a suitably sized front end isolator switch, rated at say 300A, Two suitably sized switch fuses rated at say 125/150A, and two suitably sized DB's......
A lot depends on the layout of the building. If positioning two distribution boards in different places reduces the length of the final circuits, it may be advantageous.
 
A lot depends on the layout of the building. If positioning two distribution boards in different places reduces the length of the final circuits, it may be advantageous.

It's not what happening here though is it?? The planned position of the DB is stated to be 10 metre's away...
 

Reply to TNS and 315a bs88 in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

  • Question
Thanks mate this helps a lot, especially with the 2 board but real life scenario they being in separate rooms
Replies
4
Views
361
  • Question
Okay, I'm struggling to find a definite USA definition. I see the US is a member of the IEC so I assume they use the same definitions as us??
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top