I'm the proud owner of a Victorian, 2-bed semi and recently discovered that my only means of earthing look to be my water supply and (redundant, non-conducting) gas pipe.

I managed to get UKPN to come out and do a PME availability check, having been told all sorts of things by them on the phone beforehand. Anyway, the fellas turned up and promptly fitted a PME terminal and I gladly let it continue, as it was free of charge! It was only afterwards that I realised (on phoning the engineer) that the very fitting of the PME terminal now excludes TNS as an option and that I am now committed to PME, the disadvantage being that I will now have to upgrade all the bonding which is 6mm.

My questions therefore are:

1) Given that UKPN installed PME free of charge, would they have installed TNS free of charge using the lead sheath of the cable, if the impedance was O.K? If not, then I don't care about the time/money of upgrading the bonding.

2) Would TNS necessarily require upgrading to the bonding or is this dependent on testing?

3) What are the main advantages and disadvantages of TNS/TNCS?

Thanks for your input! This is all new to me, but I have really taken an interest in it. Not least because it concerns my safety - on which note I am aware there is still no main earthing to my house as the CU is not connected to the PME terminal. Need to get an electrician round to finish, but would like to choose the best balance of practicality, safety and cost.

Jake.
 
I do not think UKPN would install a TNS earthing system now they are all hot on the PME / TNCS earthing as being a better method.
However it is not necessarily a better method, just more reliable for them to do.
TNS is good because loss of the neutral does not mean loss or earthing. It is bad because sheath decay / disconnection could mean there is no viable earth.
PME is good because you only need to send a single core sheathed cable to a single phase installation. There will also very likely be a reasonable earth since it is earthed all along the incomer back to the substation. Disconnecting the neutral does mean that you have lost all earthing for the installation which is why bonding becomes so important.

Although you now theoretically have bonding that does not comply with the current regs this does not necessarily mean you must upgrade it if it is still adequate for the installation.

You do need to get a main earth to your CU as soon as possible , presumably UKPN just provided a main earth terminal from the head for this purpose. But (as it is not their area of work) did not provide a CU earth!
 
with PME, the minimum size of main bonding conductors is specified as 10mm . however, on an existing installation, if the 6mm bonding shows no sign of deterioration, and is verified as connected correctly, then it may well be that it can be left. your electrician can confirm this.
 
with PME, the minimum size of main bonding conductors is specified as 10mm . however, on an existing installation, if the 6mm bonding shows no sign of deterioration, and is verified as connected correctly, then it may well be that it can be left. your electrician can confirm this.

I thought this would have meant if an existing PME installation showed no signs of deterioration of the 6mm bonding then no need to upgrade. But this is now a new PME instalation so I think it would need to be upgraded. but as you say his sparks can confirm it.
 
Cheers guys,

I had posted a picture and more info but it said the moderators need to check my message first. I'm new on this forum so don't know when that message will appear if at all!

I'll double check with my spark, although he mentioned 10mm so must lean that way. He's gonna stick an RCD in too. Said if buy one they'll connect it! What would people recommend? He had just said "63A RCD" but UKPN installed a 100A fuse now.

Also, any issues with finding space for the 16mm earth on my old, 4-way Wylex rewireable fuseboard (to connect to earth block)?

Apologies for repetition if my other message gets posted too.

Related question: does supplementary bonding have to be bonded itself to the earth from a nearby circuit?

Many thanks.
 
Cheers guys,
I'll double check with my spark, although he mentioned 10mm so must lean that way. He's gonna stick an RCD in too. Said if buy one they'll connect it! What would people recommend? He had just said "63A RCD" but UKPN installed a 100A fuse now.
You will have to check with him on that one because I do not know the method he is using to do this.

Also, any issues with finding space for the 16mm earth on my old, 4-way Wylex rewireable fuseboard (to connect to earth block)?
Should be OK, even if the cable needs to be fed to two terminals.Though sometimes the holes are a bit small and there can be a lot of CPCs in the earth bar.

Related question: does supplementary bonding have to be bonded itself to the earth from a nearby circuit?
Yes
Hope it all goes well.
 

Reply to TNS or TNCS - which is preferable? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Indeed it is clearly marked as a PME earthing system, which means it is TNCS.
Replies
5
Views
3K
loz2754
L
  • Question
Also the EVSE must not be on a shared RCD which it is.
2
Replies
44
Views
9K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
832
Shhh, don't tell the Chinese they want a bit of the action.
Replies
1
Views
497

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks